PLC5 : Connecting differential output instrument to single-ended card
johny-rock
Nov 2010
Chambly
Hi all,
I have a PLC5 rack that is actually full(No place for an aditionnal card). The rack has a couple of spare inputs on 1771-IFE cards and I need to hook up an instrument that requires a differential input.
Since AB documentation tells not to mix "singled-ended" and "differential" input configuration on the same card and all of them are configured as "single-ended", I was asking myself : Is there a way to connect a differential output instrument to a single-ended input using a converter or some kind of isolator ?
Thanks !
if the device supplies an isolated output you *may* be able to hook up it's common to the card common along with the other single ended commons. this may make it more susceptible to noise.
I was planning on using a ABB analog signal isolator.
Your answers confirmed me that it is the right way to do it.
Thanks !
We have an old PLC5/25 with 6 racks spread over 4 cabinets. At some time past they tried to connect a DL20 ans 3 DL10 displays to it. The...
1,913
As the title indicates I am trying to connect a PLC5/40C to Honeywell Experion R301 using 1785-ENET card. I am not really familiar with PLCs at...
2,994
I am using the following formula and I am getting error, Invalid Expression - too many closing parenthesis. when i copy the formula to notepad or...
158
Preface: Kinda long, so I made section titles Intro: I just want to see if anyone here has seen anything similar. A PLC5-40 series C enhanced...
377