Sinking/Sourcing Input Outputs
luisarcher
Jul 2017
Montréal
Hello again guys,
I've read tons of informations on sinking and sourcing inputs and outputs, however there is something bugging me with this.
I want to connect a Banner TowerLight to my PLC to light its light (fun incomming). Here is an image of the wires:
I have my output card, which is a SOURCING one. Therefore, I know that my output card will send current to the towerlight to light its light. So, I think that I should go with the sinking connection, so NPN.
However, I check the picture and I don't understand how it works. I will connect my pin 3 to my 24 VDC and the rest of the colors (pin 4-1-2-5) will be connected to the PLC outputs. So, when I will activate my output, it will send current to the colors but where will that current sink if my blue cable (pin 3) is connected to the 24 VDC ? Shouldn't it be connected to the ground ?
Thanks a lot,
luisarcher.
If your output card is SOURCING its providing a path to the + side, so you would use the PNP labeled diagram.
That was what I thought after thinking it for a bit, but I find it odd that Sourcing and PNP go together.
Thanks a lot guys !
In reality if you look at that diagram, all it is telling you is that the lights don't really care which direction the flow goes. All it is saying is that whichever side is +, the other side is -. So whatever you use as the Common in your PLC output card gets connected to terminal 3, the individual outputs then go to the other terminals.
I overthought this once too .
These lights are our standard light towers
Current is either going left to right, or right to left.
Hook wire three to your-24 on the power supply
Hook the positive +24 to the comm on the card and wire in you assigned outputs
Just think of it as a light switch. Right? All your doing is passing current.
The "problem" is the diagram is trying to be helpful and showing you how to wire to "sourcing" output and you are overthinking it. As most of the people here did, I usually just look for the common and that tells the story. "Sinking" and "Sourcing" are not all that helpful or intuitive to me.
You are unnecessarily confusing the issue by thinking in terms of "sending current" to the lamps. You will create current flow through the lamp when you apply a voltage to it, whether you use a sinking or sourcing output module. The only difference is whether you are doing the switching on the positive or negative side of the circuit.
Sourcing outputs unconditionally connect the negative side of the power supply to the load while switching the positive side. Sinking outputs unconditionally connect the positive side of the power supply to the load while switching the negative side.
There is some inherent confusion built into discussions of current flow because electronic drawings use symbols based upon "classic" current flow, which is from the positive to the negative side of the power supply, although we all know from basic physics classes that current actually flows through a load from the negative to the positive side of the power supply.
Unless, of course, you are discussing hole current within a transistor -- but that's another discussion altogether. ;)
Good morning all. I have never seen this done but I want to ask if it is possible. On an AB 1766-L32BWA, can you have some of the inputs wired as...
2,365
I have a client who has installed a control system which was designed offshore (ASIA), and uses a power system common to the Asian market. The DC...
1,933
I spending a lot of time for searching on this subject "sinking and sourcing input", but there are not simple answer. I want to add stop/start...
7,092
O
what is a sinking or sourcing input/output means?
4,102
Hi there, I have a 2 wire npn sensor. For example in this diagram: I'm guessing i should connect it to a PLC dc sourcing input as such? Would...
5,218