Sinking transistor outputs
Lc1
Jan 2014
Uk
59
I have a cpm1a that has sinking transistor outputs. I have recently used this to power a relay coil. The relay coil is energised as soon as I wire it in and switch on the plc. The output status indication light remains off. Has anyone came across this before?
Its possible for solid state leakage to do this. It depends on the relay. Is it a solid state relay?
Relay "coil" grounded?
It’s a 24vdc relay coil,not grounded. I’ve tried it on the first two outputs and it does the same thing, not sure what is happening as I can’t force the output on/ off from the plc program either.
Can you install a interposing relay with dry contacts between the PLC and your 24v relay?
Just to test the leakage theory.
I will try it. Need to get another relay first. Just bought one relay to mess around with.
I'm guessing it's mis-wired.
Omron CMP1A transistor sink output sinks current from the perspective of the load, not from the perspective of the channel's transistor. The relay's A1 or (+) terminal should connect to the output channel, and the relay's A2 or (-) terminal should connect to the module's COM terminals.
Yes that’s the way it’s wired. Just went and double checked. I’m now not getting anything from the digital output and the relay is not energising. I’m maybe thinking it’s an addressing issue. I am assuming that first output is 1.00 and second is 1.01 third is 1.02 and so on. Really not sure what the problem is.
Hi.
I have the power supply v+ connected to terminal A1 of the relay. Terminal A2 is connected. to the channel. The power supply V- is connected to the com.
Not much left, other than the stuff we're certain you checked.
PLC bad. Not in Run. 24VDC low. PLC is Sourcing, not Sinking. Does this PLC have a diagnostic mode where all outputs are off?
Inputs working, and you can see them on the PC?
That is an old PLC. 1.00 is an input not an output. Check the manual but I think outputs start at 10.00 - have not seen one of them for many years. Make sure the relay has a flywheel diode in it.
I’ve got some devices that are triggered by shorting pins to common. There is 24 volts on each pin and right now I am using a relay output card...
2,587
Hi, I am working on a project with Delta PLC for the first time. I want to connect a Sinking analog sensor (4-20 mA) to a Delta analog module...
1,665
Good morning all. I have never seen this done but I want to ask if it is possible. On an AB 1766-L32BWA, can you have some of the inputs wired as...
2,366
Intern here, I have been tasked with setting up a 24V Keyence vision system. Looking at the control prints, the existing input signals are sinking...
1,817
I have a client who has installed a control system which was designed offshore (ASIA), and uses a power system common to the Asian market. The DC...
1,933