Siwarex Module
saytunak
Jan 2009
Orissa
can any one tell me ,how siemen's siwarex module is directly connected to the load cell.what about the load cell excitation volages.
Dear,
i want to know the connection details of siwarx module to load cell. as we know, load cell has 6 cables and how these cables are connected to the siwarx card.
Hello
Depends what exectly SIWAREX module you'll use, go in Google and search for manual. There you'll find this information.
regards
Dear,
Do you have the siwarex card wih you?
Is it a 200M module or 200S ?
If a 200M open the door there the connections are explained
Like followed
Output +/-
input +/-
Sense +/-
That would normally be the same like your loadcell wires are named.
If i remeber well with a 2 channel card Channel 1 is on the bottom and channel 2 is on top.
With ET200S it stands on the module that you click on the base
Some tip
1.If you have more loadcells for the same weight application then you can put the wires that are marked the same together and connected them as 1 wire on the siwarex
2.(I better check this first but ok)
If you would have a 4 wire loadcell you can make it a 6 wire loadcell by bridging the signal to the sense.
Good luck
We are using many Siemens siwarex weighing module. Sometime one of them indicates"sf" error and after replacement of that particular module system...
2,016
We are using many Siemens siwarex weighing module. From sometime one of them module shows "sf" error and after replacement by spare module...
1,110
WELCOME EVERY BODY. What is different between 4 wire and 6 wire connection for siwarex wl 230 rated load 10KG ???????????????? THANKS
1,998
Hello, I have problem with signal converting from Siwarex-M module in Simatic S5-115U. Siwarex-M module 7MH4553-1AA41 is placed in ET-200 rack...
3,353
Gents: I have a S7 315-2 DP PLC with several IM153-1 Racks. I have 4 Siwarex U Weighing Modules in one of the remote racks. I am using a SFC 58 to...
5,956