sizing overloads and fuses

mcalidl

Member
Join Date
Aug 2006
Location
Birimingham, AL
Posts
50
I am a young engineer and have a simple question. I am putting a 6KW 3 phase 480 v heater on a size 1 starter. I know this will work on a size 0 but that is not very common around here. I have a question about properly fusing and setting the overloads. What size and how do I go about figuring this out. Which one is instantaneous and which is time delay?
 
Find yourself a copy of the US electrical code (sorry I don't have one in front of me). Overloads are for motors, you need branch circuit protection for a heater.

You can calculate the current for the heater using the formula.

P=Sqrt3 * EL * IL

IL= 7.3A

Follow the code from there
 
mcalidl said:
I am a young engineer and have a simple question. I am putting a 6KW 3 phase 480 v heater on a size 1 starter. I know this will work on a size 0 but that is not very common around here. I have a question about properly fusing and setting the overloads. What size and how do I go about figuring this out. Which one is instantaneous and which is time delay?

I do not know about regional dialect but the OP did state size 1 starter; which usually references NEMA motor starters and heaters are a common term for the overload elements. There can be crossover points between starter sizes but all should be relevant to the motors FLA and class for the overload protection.
 
mcalidl said:
I am a young engineer and have a simple question. I am putting a 6KW 3 phase 480 v heater on a size 1 starter. I know this will work on a size 0 but that is not very common around here. I have a question about properly fusing and setting the overloads. What size and how do I go about figuring this out. Which one is instantaneous and which is time delay?

all of the info requested is calculated using the motor nameplate data. The overload may fit physically, but to be properly 'sized' is another matter. The FLA of the motor will determine the size of fuses & overloads required. Instantaneous & time delay uses are as diferent as manuacturers.
 

Similar Topics

Hello, I have a question about fuses and how to calculate their required size. I understand that determining the appropriate fuse size isn't...
Replies
0
Views
157
Specification of Codesys is being driven by customer and I'm being asked to control roughly 100 network connected vfd's for a conveying project in...
Replies
12
Views
3,174
Good Morning , We have a 100 HP , 480 V (Full Load Amps 124 ) Hammer Mill motor that has a Wye/Delta starting procedure. I would like to put...
Replies
16
Views
4,260
I have 120 VAC feeding a Micrologix PLC. I am feeding my I/O with 24 VDC using a power supply. If I add up the current draw of all I/O, I get 5...
Replies
14
Views
4,679
Hello! I have a question regarding the HMI in InTouch, almost a month ago I made an HMI and I have not used it again, now I need to make changes...
Replies
6
Views
2,048
Back
Top Bottom