We have 2 SLC-150's (each with 2 expansion modules) and they have worked flawlessly for 10 years. A few weeks ago one had a CPU fault so I used PCIS software to clear the processor and load the program back in and went back to RUN mode. Then a couple days ago another CPU fault occured (I'm off that day) so someone else basically does the same thing.
The SLC-150 has an Eprom (1745-M1) that has a copy of the machine program. We just realized the first rung does not have the (864) element which is supposed to allow the eprom to fill the nvram if nvram is bad. The SLC-150 has no battery backup but I think I read somewhere the internal capacitor might maintan nvram for up to 2 weeks?
The machine power is usually turned off over the weekends so the capacitor (or maybe the eprom?) has been working fine for almost 10 years!
We don't have the handheld controller which would help in determining the fault code (I don't think PCIS will report the fault code?)
I just purchased a handheld controller, spare M1 eproms, backup batteries and spare SLC-150 and expansion racks. (production management has gotten a little worried after these 2 events!)
So, am I missing anything?
thanks!
Fred
ps: Can Rung comments be entered using PCIS? (I can enter element descriptions but can't enter rung descriptions)
fredm54 said:
...am I missing anything?
Yes. An upgrade to a ML. 🍻 If you can swing it, do it. If management is nervous enough to purchase a backup then they should be looking a little farther down the road and upgrade to a supported product.
To put in a rung comment in PCIS, place your cursor on the + character at the beginning of the rung on the left rail, then press the F9 key. A cursor will appear at the end of the rung number and you can type your comment.
|RUNG: 001 <---Comment starts here
put cursor here -->+----] [-----------------------( )---
and press F9 |
How can I get a schematic for it? I am unable to communicate to it using PCIS with a 486 PC and suspect the SLC150 to be faulty (found in a junk...
3,163
HELP! I've been searching & searching for the software to run my SLC150 PLC for DOS 6.22 and for some reason, every link I have found for it -...
1,177
Hi, I have an old SLC 150 processor that is throwing up a CPU Fault light. I have an EEprom program chip for it, but I can't get it to load up...
2,386
We have 3 SLC-150s that we are using, we would like to create a print for them and diagram the program so when we get approval we can replace them...
2,711
Hello, I am completely new to PLC's (and forums) and have been tasked to repair/upgrade a conveyor system at my college. It currently has an Allen...
2,721