SLC 5/03 Flashing Fault When Switched To Run
Jun 2016
Addison IL
I have a palletizer in production that hasn't been run for a few years. I was tasked with getting it running and the 1st thing I noticed was that the battery had died and the program was lost. After changing the battery, I was able to get a backup copy of the program downloaded, the only problem now is that when I turn the key back to run, I instantly get the flashing fault light. I also have lights on all the input modules but nothing is lit up on the output modules. I keep getting the fault message" the required memory module is absent or S :1/10 or S:1/11 is not set as required by the program" Any help would be much appreciated!
See pdf for status bit settings.
Do you have a memory module?
Set status bits to match your system requirements.
You're alright Mickey! The Status bits S1/10,11, and 12 were in the wrong configuration, 1,0,0. Changed to 0,0,1, downloaded once more and its up and running. Thanks again!
Hi, I just bought an allen bradley 1747 10 slot rack, PSU, CPU, input & output modules. I also bought one of these to connect my a usb port on...
19
26,928
188
110
121
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
128
