SLC 5/03 - HMI/PLC Connection

rajy2r

Member
Join Date
Nov 2006
Location
Canada
Posts
167
Customer has a SLC 5/03 with some custom HMI with its own IO driver.

When the HMI is running, i cannot use RSLogix 500 as the Serial Port is "Busy".

Anyone run into this before ? Is there anyway around this ? I guess the other option would be to buy a 1747-UIC and then add another serial port. Just wondering if there is a way without that.
 
A 1747-UIC is an alternative but you have to be in front of your computer in order to use RSLogix 500. May be the best option is to interface HMI to slc using DH485 port and leave slc serial port free to be used with rslogix 500 and df1 protocol.
Another alternative is to use a 1762-net-eni this module converts slc500 serial port into an ethernet port. This way you can use your software and HMI at the same time but you have to change your HMI interface from serial to ethernet. BTW you will need a data comm switch too.
 
The 1747-UIC is a good way to go. I think it’s always a good idea to be at the PLC when connecting with it for programming.
 

Similar Topics

I'm looking to replace an AB PanelView 600 2711-K6C2 HMI with a C-more EA9-T10WCL. The PLC in the system is a SLC 5/03, which is staying. I...
Replies
2
Views
1,248
Does anyone know of a good HMI program that can run on Windows 7 or Windows 10 and communicate to 2 SLC 5/05 PLCs? I want to have a Info screen...
Replies
14
Views
5,012
I have a Red Lion CR10000700000210 HMI with an RS485 port that is an RJ45 connector. I want to connect it to a SLC5/03 DH485 port (RJ45). Has...
Replies
9
Views
2,704
Hello, I have an SLC 5/03 16K Allen-Bradley PLC communicating thru RS232 cable with desktop PC and this is what shows on the screen (see...
Replies
13
Views
2,523
I used to do DH+ a lot but it's been years so I thought I get a quick sanity check here. So, one of the site got a AB SLC 5/04 hooked up to a...
Replies
6
Views
2,120
Back
Top Bottom