Slc 5/03 rio scanner
RasPLC01
Sep 2011
AUS
56
I have a SLC 5/03 PLC which is already installed 5 yrs ago.now im trying to add 1 input and output module to the exisitng one
PROCESSOR is connected to RIO scanner. i would like to add my new cards to adapter side.
when i tryed to configure these cards 1746-im16 and 1746-om16
through software it is showing a message window as
identical cards dectected do you want keep same settings
yes/no
if i press yes it is not configuring correctly
if i press NO iam loosing whole existing programs
Any one can help me please?
settings
PLESE FIND ATTACHMENT
THE NEW INPUT/OUTPUT ARE SHOWN BY DOOR OPENED
Welcome to the Forum ! Thank you for posting those details about the configuration.
In SLC-500 controllers, the "Racks 1, 2, 3" that are configured in the I/O Configuration applet are the "local racks"; you can connect up to 30 slots using backpane connector cables and separate chassis and power supplies. These cables are only about 1 meter long.
Do not add your new modules to that configuration, because they are located in a RIO network adapter chassis, not in an extended Local chassis.
The configuration of RIO adapters is done with the "1747-SN G-file Configuration" window, which you have also shown.
The key to understanding Allen-Bradley nomenclature is to know that one "Logical Rack" is 8 "Groups", each of which has 16 bits of Input Data and 16 bits of Output Data.
My guess is that the eight-slot chassis you showed in "AdapterSide.jpg" is the one represented as "Rack 00", size 1/2 Rack.
You must make two changes:
1. For the 1747-SN Scanner Configuration, change the configuration of Logical Rack 00 from 1/2 to 3/4 Rack size.
2. For the 1747-ASB configuration, you need to change some DIP switches.
Set SW2-7 = OFF and set SW2-8 = ON to change the ASB Module Image Size from 4 Groups (1/2 Rack) to 6 Groups (3/4 Rack).
The configuration of the 1747-ASB module image size is shown on page 4-10 of Publication 1747-UM006. All Allen-Bradley user manuals are downloadable in PDF format from the literature.rockwellautomation.com website.
The new modules data will be in the SLC-500 I/O data table as addresses "I:1.4/00-15" and "O:1.5/00-15".
Thnk you very much ken
all i need to do is change these 2 settings.it will automatically configure new i/o modules
and
any problem by complementry mode?
i need to communicate slc 500 with RIO and how i configure it thanks
2,301
Due to all the recent icing from the great winter weather this past week we have experienced many power glitches. reaking havoc on our drive and...
4,788
I am using SLC 5/05 processor with remote I/O's with 1746-ASB module. The remote rack has two RTD cards. One is working OK. The another has 4...
5,888
I’ve searched the internet for answers on how to do this. But I’m in need of some help. I have a slc 500 connected to a RIO. There are two racks...
1,148
I am getting an error on my 1747 - ASB that says NOC. I looked this up in the manual and all it says is no communication. Which I knew that lol...
1,637