Guys,
I have this remote rack communicating with a SLC 5/04. There are several "Analog" output cards in this RIO that are being used to control VFD's on blower fans through a 4-20ma signal.
I have one of these cards that channel 3 is not varying the 4-20ma signal going to one of the VFD at all.The value is always 4.36ma
I already confirmed that the 1746-NO4I card is good by doing a swap with another one.
I also checked the PLC code to make sure that there was no issues in it.
Do you guys think that the actual rack for this RIO could have a problem which affects that particular channel?
Also, the VFD (Allen-Bradley 160 SSC) always display 50HZ in the front screen even do the 4-20ma signal is not working. I checked all parameters against other equal VFD's that are working and I can not find any differences between them.
Jose:
1) Disable analog output in the plc program, then create a new rung where you move several values one at a time to the same analog output while measuring with a 4-20 mA meter. If that is working then you have a problem with plc program.
2) If the vfd is showing always 50 Hz please then check VFD I/O, it´s posible that vfd is using fixed speed regardless of 4-20 ma signal.
I too think its running at a set speed. I assume the 4.36 is max set for the drive to catch up to? I would do the recommended rung test too.
Hope this helps! J
Are you sure the analog command is wired to hte right input on the drive? 4-20mA signals should be wired beween terminals 3 (common) and 4. This is how the drive would react if you have a current signal feeding a voltage input.
Keith
Thank you guys,
Widelto, you are suggesting to turn off the piece of code that sends the 4-20ma currently to the 1746-NO4I card and then manually put numbers that represent current amd measure with a meter, right.
A quick update that I feel soo embarrase to report but it turn out that the 160 drive we had controlling this blower motor was the wrong one. The 160 drive was a "Preset Speed" model instead of an "Analog" model.
When I was measuring the amps going into the VFD, I just broke the loop between the VFD and the 1746-NO4I card and added the meter and due to the wrong type drive it was causing the strange behavior on the 4-20ma signal.
Hello, I've got a project where I need to get information from two ABB ACS880 VFDs onto the plant operator's screen (or alternatively, onto...
23
2,642
My DeviceNet skills are rusty and weak... so of course, an old, obsolete Reliance 400 HP VFD goes down and we're looking at replacing it with a...
5,018
Good day all. Another first for me. I have attached a project of a system that is in operation. It has an Allen-Bradley 160 SSC VFD that is used...
2,836
I setup a pump control system awhile back. It had two motors, two VFD's 1336 PLUS II, two Scanport modules 1203-EN1, and a SLC 5/05. This all...
4,291
Hi, has anyone ever connected a slc 5/05 to a powerflex 700 vfd via the ethernet port on processor. The vfd has a 20-comm-e communication module...
8,613