Good day all. Another first for me. I have attached a project of a system that is in operation. It has an Allen-Bradley 160 SSC VFD that is used by a crane to traverse from one tank to another. The control for the crane are on Ladder 2, beginning at rung 21, near as I can tell. What I need to know is this: How exactly does the PLC control the drive? I'm not able to connect my laptop to the PLC and run the crane, because of the dangers in the room. I can only do it with production stopped and that doesn't happen very often here. Otherwise I would just operate it and watch the ladder. The operators pushbutton is connected to a 1746-IA16 input module and the outputs go to 1746-OW16 module. It is a 5/04 CPU. I'm not concerned about the lift/drop inputs and outputs, only the traversing control. The wiring for the VFD from the output module is, O:5/0= Forward, /1= Reverse, /2= Travel SW1 (low speed), /3= Travel SW2 (medium speed), /4= Stop, /5= SW3 (jog). Any help you could be, as always, greatly appreciated.
You need more info. How do you command the carne?
Can you list the inputs for the commands?
Is there a drawing?
Pendant control
I:4/0= Forward, /1= Reverse, /5= Bath occupied, /6= Emergency Forward Stop, /7= Emergency Forward Slow, /8= Emergency Reverse slow, /9= Emergency Reverse stop, /10= Forward slow, /11= on station, /12= Reverse slow, /15= base position
Drawing for VFD or for the hardwiring of my input and output module?
The PLC reads the input data table (including the hoist pendant PBs configured inputs I:4/0, /1, /2, /3, /4, /5, /6, /7, /8, /9, /11, /13, /14), executes the ladder logic and then fills the output data table with the results of the scanned logic.
Outputs O:5/0, /1, /2, /3, /4, /5, /8, /9, /12, /13, /14, /15 are wired up to the VFDs corresponding/configured digital inputs, effectively controlling the operation of the device.
Attached is a drawing of the hard wiring between the output module and the VFD.
I see a couple of issues with your wiring diagram.
According to it, the VFD's 4-20 mA analog input terminal is wired up to a relay output passing the voltage carried by wire 38; the same for TB3 Terminal 1 (which is normally fed with 10 VDC by the drive's internal power supply).
If this is accurate, then the drive's control circuitry is most likely damaged.
Besides the above mentioned issues, LAD 2 of your RSLogix 500 application file answers the original question and your wiring diagram supports it 100%.
Search for every hoist function designated PLC output OTE (Slot 5 1746-OW16 Relay Output- O:5/x, y, z, ...) and the logic related to it will explain the programmed functionality.
I have a program that I've used 100 times. SQO settings: File N7:0, Mask 0FFFFh, Dest B3:1, Control R6:0, Length 8, Pos 2. Length & Position...
48
978
Everyone, i am in the process of purchasing the Slc 500 version of software to support what we have and i have a question. Several of our...
775
In a slc 500 plc I am trying to move data with out using a lot of moves. I want to move data from n7:1 to n7:2 and data that was in n7:2 to n7:3...
1,367
Customer has a circa 2004 SLC-500 PLC. Fieldbus is a 1747-SDN DeviceNet scanner. Customer has SLC-500 file (.rss) with no comments. Has no *.dnt...
564
After I tried wiring, I used computer program communication to read the PLC N value, but received a NAK signal. And the DL3500 CHA light keeps...
431