Hi all
I have a legacy PLC (1747-L552C) and I have been asked to look at remote access (it's communicating via ethernet to a PVPlus6). I have an e w o n flexy VPN router and looking through the manual for that I need to add the e w o n IP address as the gateway in the channel config. of the SLC. Currently this is all 0s, will I have to stop and restart the processor after I change the gateway?
Thanks in advance 🍻
You shouldn't have to, in both cases.
That is, you shouldn't have to set the gateway address in the SLC to the IP address of the e w o n for it to work. I've got a client who carries around an e w o n Cosy whenever they go to site, and if they need support, they plug it in and I remotely connect and go online. None of these PLC's have had the gateway set to whatever IP address the e w o n is using. I'm not sure I've ever used it to get online with an SLC specifically, but I can see no reason it would be any different. Try it without setting the gateway in the SLC and see if it works.
And as to whether the SLC will need to be stopped and started - again, no, you shouldn't need to. IP settings in my experience can be changed on the fly. Sometimes I've had issues where I can't change a gateway setting because the device has an active connection, and yes, in that case it's always been a case of disconnect the device from whatever it's talking to, power cycle it, plug in directly and change the gateway, then reconnect it and let it start talking again. But that's usually with VSD's talking to a Logix PLC (or similar), and all that happens is RSLinx pops up a box and tells you that it can't do it, so there's no harm in trying. Again, haven't done a lot with networking on SLC's, so there may be gotchas with that specific line I'm not aware of, but I'd be optimistic.
Hello all! I have some machines that run an SLC 5/03 and occasionally a fault is generated. Recent Example: A power supply wasn't screwed in...
423
Hello, I've got a project where I need to get information from two ABB ACS880 VFDs onto the plant operator's screen (or alternatively, onto...
23
2,607
We are replacing a piece of machinery with a newer version. The new assembly has 5 TCs which are closer by far to the operator station than the...
2,258
Will a PVP7 talk to an SLC 5/05. I can't get them to talk. I have set up PVPs to Control and Compact logix plenty of times, but can't get these to...
2,507
I want to be able to use a 3rd party device to read the IO modules from an SLC505 without the use of the CPU. All the communications modules i...
32
15,259