SLC 5-1746HSCE counter card accum freeze

venkum00

Member
Join Date
Dec 2005
Location
Georgia
Posts
20
Hello,
Problem:The accumlator value in the counter card freezes when my encoder wheel spins beyond 4.5K Hz. Ofcourse the rate would be 0 at that point and previous count is also 0.
My encoder is rated for 2500PPR. I am using ring config in range mode and figured out encoder spits out 5102 pulses/meter. I used 5102 as the reset value for ring to count the length in meters.

Any suggestions ? please...

Thanks,
Ven.
 
I would use an o-scope and look at the signal going into the HSCE2. I've run much higher speed signals into an HSCE2 than 4.5kHz. I'm suspecting you will see some serious slew on the encoder signals. Also, are the HSCE2 jumpers set to match the encoder voltage?


Keith
 
bernie_carlton said:
What accruacy do you REALLY need? That should help choose a lower PPR encoder.
Bernie, I am sure 2500PPR is an overkill, but we have those on several machines. The HSCE is rated to handle up to 50K Hz. I do not see a problem in that??
 
I am using 1746 HSCE card and YES the jumpers are in correct position. no signal issue either.

Any other suggestions??

thanks.
 
if you have scope, check the signal. if the encoder works on low speeds nut doesn't on high, cabling is first to be checked. i've seen so many systems where designers had treated analogs or high speed signals like regular sensor wiring... (n)
 

Similar Topics

Hi, I have been asked to modify a machine as follows. On site there is a SLC 5/02 plc (1996), with spare slots. I am using RS logix 500 V5.20...
Replies
2
Views
3,492
I’m attempting to send a temperature from a SLC-5/02 to an EZiMarquee display. The vendor said to use a MSG instruction to send the data to the...
Replies
1
Views
96
Hello all. I have a few SLCs in my plant and of late we've seen a weird issue: The system will be running normally and then randomly the outputs...
Replies
2
Views
104
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
Replies
3
Views
114
I have a redundant ControlLogix being set up. This program reads a value from a remote site which happens to be SLC PLC. Rockwell mentions SLC...
Replies
2
Views
104
Back
Top Bottom