I have the pleasure of converting a very large SLC program to Studio 5000 for an L81E processor. To cut to the chase, I've come across many COP instructions where the copy is an Integer into a Float. I've heard a little scuttlebutt concerning the difference in the new processor being that the length is based on the "Destination" as opposed to the Source in the SLC COP Instruction. I've the luxury of having an SLC 5/05, CL L62, and CL L81 on the rack and have tested the same instructions across all the processors. The results on the CL processors are identical but different than the SLC Processor. I have a hunch why this is, but I'm looking for a solution for how to convert these instructions to get the intended result from the SLC. FYI, I believe the SLC was doing this in order to "pack" and "Unpack" Floats from devices over device net, as I understand it uses only Integers?