Hi all.
I have an existing customer that has a need for updating the program in the SLC L551 CPU. The update is nothing more than a change of the IP address.
The updated program is stored in RAM memory at the moment, but I need to send an updated EEPROM so that they are safe.
Problem is that I dont have an L551 (16kW) CPU available, but I do have an L552 (32kW) CPU.
Question is: If I generate the EEPROM in the L552 CPU, will the program on the EEPROM run in the L551 CPU ?
Thanks in advance.
NB. I dont know how to put this in a search string, so no I havent searched already. Apologies if it has been discussed already.
Answer is YES, you can.
Have a look to the User Manual, starting page 44:
You can burn a program into an EEPROM memory module using a processor that is the same or different from the one used to run the program.
Anyway, there are some considerations and limits, the manual explain well all the possible combinations thru a table.
Hope this helps.
- fuzzy logic
Hi friends, I have a Slc 5/05 1747-L551 processor that is communicating (was communicating) with a panelview 700 plus 2711P-B7C4D1 thru DF1. Bubba...
6,410
Hi guys, I've got a SLC 5/05 1747-L551 processor here that won't talk to me. The Fault light is flashing red, the Ethernet light is solid...
16,070
Hello fellow techies, I am using a BSN modules to switch RIO on a redundant SLC500 project (I didn't spec the hardware). The design has one pair...
17
16,078
I’m attempting to send a temperature from a SLC-5/02 to an EZiMarquee display. The vendor said to use a MSG instruction to send the data to the...
95
Hello all. I have a few SLCs in my plant and of late we've seen a weird issue: The system will be running normally and then randomly the outputs...
103