Hey all,

Recently one of my SLC 5/04's (L542B) has started losing its sequence when it's powered off. Until recently the system could be powered down and back up again without issue. I've looked at all the coding and the areas effected are all latch/unlatch instructions.

This is really stumping me, no program changes have been made to this area of the program and other PLCs in the plant don't seem to lose their place. We are in an area extremely prone to power outages and surges so this is coming somewhat of a severe issue.

Any ideas?
 
Thanks for the link but I don't think the situation is the same. The processor has not once lost its memory or had a major fault, it just seems to lose it's place in the bit logic. There is no EEPROM in the processor so I know the program is not being lost.

I know back when I was learning PLC5, there were settings for each N/B/etc file as to how it behaved when a power loss occured. You could set it to protected or redundant or something that would cause it not to be reset on powerup. Is there a setting such as this in a SLC?
I will have our electrician double-check the grounding on the plc tho.
 
Frequently when electrolytic caps fail, they get high leakage. The visible symtom is they get hot. They still work somewhat when hot, but are way out of spec when cold.
This creates the symtom of "It stars working after it warms up". The only thing in today's electronics that starts working after warmup is electrolytic caps.
Follow baxtersdad advice and replace the power supply. That power supply is going to totally fail very soon.
 

Similar Topics

Whenever we lose power to the the machine, the PLC loses its program. But as you can see in the picture, the battery fault LED is not ON. Also...
Replies
13
Views
4,738
our SLC5/01 (1747-L511) keeps losing program whenever there is power outage. There is no battery LED warning light. There is no EEPROM. Don't...
Replies
5
Views
1,961
Loaded a new configuration into a 5/05 and now when we power cycle it and then I try to go online I get the attached error. And am forced to do a...
Replies
9
Views
5,043
I have an application that requires the correct time controlling of some outputs, but during testing have discovered the SLC 5/03's clock looses a...
Replies
24
Views
7,929
I have a PLC that when I powered down the electrical panel where it is located it loses the PLC code.
Replies
12
Views
5,191
Back
Top Bottom