SLC rack as RIO for PLC5
simenk
May 2010
Oslo
Hi
I have a setup with a PLC5/20E and an SLC-rack with a 1747-ASB communication module.
The SLC-rack setup is as following
slot 0 ASB-module
slot 1 1746-NI8
slot 2 1746-NI8
slot 3 1746-NO4
slot 4 1746-NO4
slot 5 1746-NO4
slot 6 1746-IB16
slot 7 free
slot 8 1746-IB32
slot 9 1746-OB16
slot 10 1746-IB32
slot 11 free
slot 12 1746-IB32
I want to use another 8 channel analog input module. When I try to insert this in slot 7, I get the error message P08.
This apparently means "I/O module placement error. the I/O module in slot 8 may have its image overlapping the image of the I/O module in its paired slot".
AFAIK, the ASB module is set to 1-slot mode, so why is this analog module overlapping its paired slot?
The configuration for the ASB is as following:
SW1
1 ON
2 ON
3 ON
4 ON
5 ON
6 ON
7 OFF
8 ON
SW2
1 OFF
2 ON
3 OFF
4 ON
5 ON
6 OFF
7 ON
8 OFF
SW3
1 OFF
2 ON
3 OFF
4 OFF
5 ON
6 OFF
7 OFF
8 ON
Thank you in advance:)
Simen
1 slot addressing means 16 bits per slot.
Slot 8 is 32Input, 16bits used from slot 8 and 16bits from slot 7 to give 32.
Slot 12 uses 16 from slot 12 and 16 from slot 11.
Slot 10 uses 16 from slot 10 and 16 from slot 9 as card in slot 9 is an output card so input bits can be used for extra inputs for slot 10.
Putting another input card into slot 7 will overwite/mess with the 16 input bits that slot 8 uses, an output card could be used but not an input card.
In your program look at the input addressing for slot 7 and 8 and you should see how the empty slot is used by the 32 bit module.
I have a remote rack and intermediately the out put cards will turn off then right back on i have exchanged or replaced the following in this...
2,334
Hi, I've just started to fit a Rio Scanner to an SLC to comunicate to a RIO Adapto in an PLC2 rack I've removed the PLC2 processor and fitted...
4,650
I used up my last new Allen-Bradley SLC 5/04 controller. Does anyone have info on a good reliable place to get a new one for a decent price, or...
526
Is this possible to do on the SLC platform? The reason I ask is I would like to upgrade from a 5/04 to a 5/05 in one machine to get the use of...
1,727
HI guys, wondering if anyone has used a 1746-C9 rack extender cable to connect 2 (or more) SLC 5/05 racks when upgrading the SLC to compact logix...
3,269