Hi there. I would appreciate anyones help with the following problem ......
We have recently installed an Allen Bradley PLC system which uses a 1747-L551 Processor (Ser B, Rev 4, OS501). However with the many additions that the client had requested we ran out of user memory. We therefore decided to upgrade to a 1747-L552 (Ser C, Rev A, OS501) Processor.
When I changed the processor type in RSLogix (offline) it asked me if I wanted to resize data tables (as expected) which I confirmed, but when it recompiled the program I received the following error;
"ERROR: BTW instruction is not valid on the currently selected processor -> 1747-L552".
This message was displayed for all BTW and BTR instructions (which I use for analogue cards in my remote I\O racks through 1747-SN & ASB modules.
I realise that Block Transfer instructions must still be supported by SLC processors but can find no reason for the messages.
regards
Steve
We have recently installed an Allen Bradley PLC system which uses a 1747-L551 Processor (Ser B, Rev 4, OS501). However with the many additions that the client had requested we ran out of user memory. We therefore decided to upgrade to a 1747-L552 (Ser C, Rev A, OS501) Processor.
When I changed the processor type in RSLogix (offline) it asked me if I wanted to resize data tables (as expected) which I confirmed, but when it recompiled the program I received the following error;
"ERROR: BTW instruction is not valid on the currently selected processor -> 1747-L552".
This message was displayed for all BTW and BTR instructions (which I use for analogue cards in my remote I\O racks through 1747-SN & ASB modules.
I realise that Block Transfer instructions must still be supported by SLC processors but can find no reason for the messages.