SLC Upgrade gives program errors

woodward_uk

Lifetime Supporting Member
Join Date
Mar 2006
Location
Hinckley, Leicester
Posts
42
Hi there. I would appreciate anyones help with the following problem ......

We have recently installed an Allen Bradley PLC system which uses a 1747-L551 Processor (Ser B, Rev 4, OS501). However with the many additions that the client had requested we ran out of user memory. We therefore decided to upgrade to a 1747-L552 (Ser C, Rev A, OS501) Processor.

When I changed the processor type in RSLogix (offline) it asked me if I wanted to resize data tables (as expected) which I confirmed, but when it recompiled the program I received the following error;

"ERROR: BTW instruction is not valid on the currently selected processor -> 1747-L552".

This message was displayed for all BTW and BTR instructions (which I use for analogue cards in my remote I\O racks through 1747-SN & ASB modules.

I realise that Block Transfer instructions must still be supported by SLC processors but can find no reason for the messages.

regards
Steve
 
Last edited:
Make sure you select 1747-L552C, not 1747-L552. The "not-C" versions do not support BTW/BTR, but "C" versions do. You have to select the right processor in the controller properties. (I just tested it and confirmed this...)
 
Thanks Guys

As you said I had selected the first 552 that was visble in the drop down list, the Series C was further up and out of sight. Trying to do too many things at once!!!

thanks again

Steve
 

Similar Topics

Looking into maybe upgrading a SLC 5/05. 13 Slot rack. 12/13 populated. DeviceNet to a panelview. That's going in the bin, replaced by...
Replies
40
Views
2,570
I recently came aboard a new company. They (or we I should say) have a critical robotic process line that has an infeed conveyor section running...
Replies
7
Views
1,726
I have a customer running the above. Its about a 10-15 year old installation. They would like to upgrade the SLC 5/05. I would probably use...
Replies
5
Views
2,540
HI guys, wondering if anyone has used a 1746-C9 rack extender cable to connect 2 (or more) SLC 5/05 racks when upgrading the SLC to compact logix...
Replies
6
Views
3,294
I have a customer that has several L36ERM's running SLC's racks (A13's) via AENTR, yesterday I was working on their SLC as they had a NR8 fail...
Replies
5
Views
2,260
Back
Top Bottom