Slc500-1746-no4i
shazad5444
Feb 2014
Houston
126
Dear Friends, Need your expert opinion. We have SLC500 and installed Analog Output module is 1746-NO4I. Scaling and PID configuration is 0~16383. We observed that PLC out out is not more than 16 mA at 16383. Please advise how to increase module output upto 20 mA. Didn't find any configuration of 1746-NO4I.
the PID for your platform ALWAYS has a range for its output signal as 0 to 16383 ... but ... the analog output module that you've mentioned needs a scaled signal of 6242 to 31208 ...
so ...
most people use an SCP instruction to calculate the difference ...
here's a link ...
https://literature.rockwellautomation.com/idc/groups/literature/documents/um/1746-um005_-en-p.pdf
(from top of the Google search list) ...
hope this is helpful ... good luck with your project ...
Thank you very much Ron for explaining. Please let me know is there any option in RSlogix 500 to tune up PID onlune?
sorry but RSLogix5000 is the only Rockwell platform that offers an "Autotune" feature ... (for some processes it works OK - for others - not so well) ...
suggestion: if you're allowed to post your new program file online - then zip it first and attach it to this thread ... we'll be happy to take a look at it for you ... the most common "problem areas" for PID control are the input signal scaling and the timing/triggering setups ... be sure to attach the ENTIRE project file (RSS extension) not just screen shots of the PID rung ...
I have two output cards sitting next to each other in a rack: 1746-OW16 1746-OW16 (Octal) output 13 in the first card triggers a solenoid. When...
2,210
PLC SLC5/04 is runing with 1746-NO8I but this module is got defective How can i Use 2 module of 1746-NO4I instead of 1746-NO8I? kindly Help
1,886
I need help in identifying the fault with a 1746-NR4 RTD / resistance module. The hardware is a SLC500 1746-NR4 module inserted into slot 3 of a...
1,295
Here's what I've got... SLC504, 1746-OB16 (Transitor) DC sourcing output module. I'm planning on powering small solenoids with this (I...
3,293
hi i need help in this problem unit slc 500 -1747-l542 give alarm -dh+01:u nable to communicate with remote station the unit allen -bradly conect...
1,851