I need help in identifying the fault with a 1746-NR4 RTD / resistance module.
The hardware is a SLC500 1746-NR4 module inserted into slot 3 of a 10 way rack, the processer is a SLC500 5/04

I have been using the RTD module to sample the temperature of a beer-brewing kettle and a fermentation enclosure, tone of the RTD’s was used to control the cooler, the second RTD was scaled through logic and controlled a temperature element through PID logic, this has been running fine for some time.
Recently I returned from work and found that the CPU had faulted, the error was on slot 3 (RTD module), unfortunately I didn’t write down the error code, but I’m sure it was xx61, I know now I should have paid more attention to this code.
When I cleared the error the processer ran perfectly with no new errors, what wasn’t right was that the heater in the fermentation enclosure was switched on due to low internal temp, when I checked the temperature readings of the RTD against a fixed gauge, the RTD’s value read 10 Deg C and the gauge read 20 deg C.

I have scaled the RTD value directly, example I:3.0 on the first line of SCP block and I can see the temp valus on this line, I believe this to be an accurate reading. I have entered the correct configuration data in the channel configuration word, ie the correct bit settings, I have also tried to change these, example the data format values, the RTD input type, etc. When I change the data format selection the values change in respect to the original values.

Convinced that the module was damaged I replaced it with a spare that I had and inserted that, this has now become corrupted or damaged too, and on this one I have lost 3 channels? Example; When an RTD element is connected to the module on channel 2, 3 or 4 the green light blinks, but when viewed in RSLogix the channels indicates that there is a device connected? When testing the range of the RTD in an ice bath the zero went to -4 deg and in boiling water only reached 66 deg c?

I have tested both of these modules on a different PLC rack, by swapping them out with a RTD module that I know is working ok. The same fault appears with the RTD modules in either rack and with two different CPU’s.
I would like to be able to confirm that the rack or pane or rack isn’t faulty. At present there is only a D/O and D/I card in the rack.

Could this is a case that the modules require re-calibration? And is this an easy fix, can these modules be reset to the factory original spec?

I would be grateful for any assistance that could be given as I am at a loss and I think I have exhausted all avenues.
 

Similar Topics

Dear Friends, Need your expert opinion. We have SLC500 and installed Analog Output module is 1746-NO4I. Scaling and PID configuration is 0~16383...
Replies
3
Views
1,950
I have two output cards sitting next to each other in a rack: 1746-OW16 1746-OW16 (Octal) output 13 in the first card triggers a solenoid. When...
Replies
2
Views
2,209
PLC SLC5/04 is runing with 1746-NO8I but this module is got defective How can i Use 2 module of 1746-NO4I instead of 1746-NO8I? kindly Help
Replies
1
Views
1,886
Here's what I've got... SLC504, 1746-OB16 (Transitor) DC sourcing output module. I'm planning on powering small solenoids with this (I...
Replies
4
Views
3,291
hi i need help in this problem unit slc 500 -1747-l542 give alarm -dh+01:u nable to communicate with remote station the unit allen -bradly conect...
Replies
3
Views
1,850
Back
Top Bottom