slc500 5/04 ox4 error (ken roach)
shad72
Oct 2014
gladwin
induction furnace blowed a water line faulted cpu. no problem i will clear the fault move on. only light i have is fault light nothing else 5/04 series c. so i got another card put it in the slot got online no problem. problem is wrong furnace program so i cleared cpu and now it will not let me download furnace 2 program keeps telling me load from eprom because their is no program in memory. tried both keeps saying 0x4 error or no comms
Does the original CPU or the replacement CPU have an EEPROM installed ?
What firmware revisions are the original and replacement CPUs ?
What revision of RSLogix 500 are you running ?
What revision of RSLinx Classic are you running ? It sounds like you're using a 1784-PCMK card with the DH+ driver.
It sounds like the replacement CPU does have a default program; that will cause it to show up as "DEFAULT" in RSWho.
Can you explain exactly what steps you are taking to download the correct program to the controller, and exactly when RSLogix 500 gives you the "0x04 error" message ?
Is the full text of the error message "Diagnostic Status Failed 0x04" ?
If you have the equipment handy, try using a serial cable (1747-CP3 or equivalent null-modem cable) and the DF1 Full Duplex driver, to see if the problem is related to the PCMK or the DH+ driver.
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
264
can the slc500 5/05 send a email and text over Ethernet ?
189
Hello, did anybody know, if there exist an converting cable like the1492-CM1746-M01 (for an 1746-IB16 to an 5069-IB16), for an 1746-HSCE to an...
393
Customer is buying several spare 504 CPU's to have one handy when there's an issue with the ones in operation. Having them on the shelf for years...
2,847
You have to go offline to create the 'Trend' but do you have to download the program to go back Online with the Trend ?
348