I have the panel view hooked to DH+ side of 5/04 and DF1 on 5/04 hooked to ENI I can see the 5/04 but not the panelview.. I can also see the 5/05 in RsLinx
SamTheLightMaster said:I have the panel view hooked to DH+ side of 5/04 and DF1 on 5/04 hooked to ENI I can see the 5/04 but not the panelview.. I can also see the 5/05 in RsLinx
Do you need direct connection with your PV? I dont know if you can use the PLC as a passthru but odds are you only need the PLC and not the PV so the ENI is a great option
The Gateways are best option if you are moving several nodes from DH+ to Ethernet, example I just installed one that had 3 PLCs 2 HMIs and the gateway moved the DH+ network to Ethernet and that worked great... if you are needing a single node then the ENIs are great.
owner just called and said he bought some used 1769-L30ERs that are network ready. But never worked with them heck idk if rslogix500 will program them yet...
Ok so that was wasted money again
his disk is so old you cant read the serial number, cat number or anything,