SLC500 Address Confusion
glaverty
Apr 2002
Parts Unknown
509
I am working with a PV550 and an SLC 5/02 on a machine that I have been asked to make some changes to.
The address's in the Panelview are written in the form B3/58, B3/59 etc.
So I make the assumption that B3/58 = B3:3/10 which as it turns out is correct. However if you do a search for B3/58 in RSlogix it looks for B3:4/10. Why do they do this? It's zero based in the panelview but in RSLogix they skip B3:0/0 through B3:0/15 and start at B3:1/0.
This is my first project with RSLogix so to some of you this may be a known thing and for others it might be something new. Just thought I would throw it out there to see if anyone has a reason for it.
Guys follow these instructions to change your View properties
1 Select View > Properties to get the Options window.
Make sure you have a program file window opened and active (click cursor in the ladder window) or you will not see Properties listed in the View menu
2 Click the Address Display tab.
3 Make the selections that determine how your ladder logic will look on the screen display. These are described below.
4 Click OK to accept your selections.
This is the field you need to change your B Bit displays
Binary Bit Display Mode
Select /Bit to display a binary bit address by bit only, for example B3/33. Click Word/Bit to display the same address by word and bit, for example B3:2/1.
glaverty,
i've never heard of this happening before - and i DON'T doubt that you're seeing it now - but could you please go into a little more detail and tell us exactly what you're typing - and exactly where you're typing it - and exactly what you're clicking next - and exactly what happens on the screen? - i'd like to track this down - if i understand your description of the problem, then it's got to be a bug - but if it's a bug, then i'm amazed that no one has reported it before - and the search feature is working just fine on my machine -
thanks
More Confused
Sure thing Ron.
I am using RSLogix 500 Version 5.50.00.
I have a file open, I go to Search > Find and type in B3/0 and click Find All the little window pops up showing the results.
These are the results: B3/0 in File 2 Rung 2 XIC B3:1/0
It is the same file that i posted here http://www.plctalk.net/qanda/showthread.php?s=&threadid=1487 Its the one labeled "Sequencer1.zip"I just downloaded it, opened it and it does what I am describing. Try opening it and putting in the search and see what you get.
I also checked a file that Timothy Moulder uploaded a while back and it DOES NOT have the problem so it looks like it might be something with the file not RSLogix.
the problem is that a symbol (shown in green) has been defined for B3:1/0 - the symbol is B3/0 - i'm having a little trouble getting rid of said symbol - i'll let you know when i've got it -
incidentally. symbol = nickname for an address (a documentation feature)
It looks like RSLogix won't let you get rid of the symbol in ladder view.
You need to go to the Address/Symbol Database (on the bottom of the Project Tree) and delete it from there.
Once it's gone, B3/0 is searched for normally.
Ok Ron I got it figured out I deleted the symbol and that fixed the offset problem.
To delete it I went to the Project tree and double clicked Address/Symbol. Scrolled down to the one address that had a symbol and deleted it. Now when I do a search for B3/0 it looks for B3:0/0
Thanks for the Help
incidentally, B3:1/0 isn't the only one that's messed up - go to the B3 datatable and scroll along the B3:1 word - watch the symbol entry line near the bottom of the window -
anyway - the problem was that the search engine wasn't finding B3/0 in your program AS AN ADDRESS so it automatically searched for B3/0 as TEXT - and thus found the symbol -
you might find this enlightening -
http://www.software.rockwell.com/forum/rslogix/messageview.cfm?catid=9&threadid=3891
thanks to meadboba on another forum
Right but it did more than just that it offset all of the addresses for instance if you put in B3/58 it would look for B3:4/10 instead of B3:3/10.
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
283
can the slc500 5/05 send a email and text over Ethernet ?
192
Hello, did anybody know, if there exist an converting cable like the1492-CM1746-M01 (for an 1746-IB16 to an 5069-IB16), for an 1746-HSCE to an...
396
Customer is buying several spare 504 CPU's to have one handy when there's an issue with the ones in operation. Having them on the shelf for years...
2,854
You have to go offline to create the 'Trend' but do you have to download the program to go back Online with the Trend ?
350