SLC500 PLC Memory Upgrade
JerryH
Mar 2009
Tellico Plains,TN
110
I had a 1747-L542 32k processor that was only showing "3 instruction words left" for Memory Left. We swapped this out with a 1747-L543 64k processor and it still only shows "3 instruction words left".
Any idea why? We were trying to create more free memory.
No,
change the program to a 64 k processor.
at the top of the screen there are 2 checkmarks, one verifies for errors and the other compiles the program for download.
do this and save the program under a new name, then check the memory status.
james
if the program was originally for a 32 k plc and you have now specified a 64k plc, something is definitely wrong.
is it possible to goto a good backup of the program and save it as a different name and then recompile using the 64 k plc?
you might want to goto that rung with the error and delete it and see what memory is left.
james
Once in a great while, perhaps three times in fifteen years, I have had a corruption occur when switching processor types offline with RSLogix500. When this has happened, the solution has been to save the file as a SLC type, then reopen it, save again as RSS file, then try to Verify Program. This may not be the cause of your problem, as I don't recall seeing that exact error when it happened to me.
Here is the solution our local rep sent me that did the trick:
"Ok, I figured out a solution. It must have been hung up because it couldn’t recompile the project and didn’t recognize that the processor type had changed for some reason.
I changed the controller in your program back to a L542, hit Apply. Closed the Box. Pressed Verify Project.
Went back in and changed the controller back to a L543, hit Apply. And Now it shows the correct Memory."
Hi. I have a legacy project with an SLC500 PLC (SLC5/04 CPU), and we want to connect a data logging system to it. Management want to make a test...
2,700
How to connect the absolute encoder(12 bit resolution) to Hsc module of Slc500 Plc and get raw-data to my ladder logic? Please give me example...
2,712
:( any help from you pros is welcome. im running windows 7. i downloaded an emulator and that works but i cant connect to plc via laptop. Im...
1,089
Hi all. I have some SLC500 PLC and i want to protect force of signals, online edition and program download. This is possible on PLC5 but when i...
1,429
Hi friend ...... I have a problem with my plc 500 5/05..... I can go online by rs232 port but with other ethernet port can't go on line and i...
18
4,677