slc500 to compact logix conversion error
jasonelectric
Sep 2016
ontario
Hello I am relatively new and working on converting a piece of code from logix 500 to logix 5000. I used the conversion tool and it did a pretty good job but i have an issue with one part of the code where I am a bit lost. I am confused with how to translate the s:24 index register. the following is the part of code I am having issues with. any help would be greatly appreciated.
LFU(N7[50],N7[108],R6[0],10,0)
ADD(S24,50,N7[111])
CLR(N7[N7_111])
welcome to the forum ...
in RSLogix500, S:24 is the "Index Register" located in the processor's status file ... it basically functions as a location "POINTER" - and is used for instructions which have the # character as part of their address ...
the "LFU" part of your post indicates a LIFO Unload instruction ... the rest of the posted text won't properly verify on any of the systems I've tried it on ... (in other words, I can't read enough of it to figure out what it's supposed to do) ...
suggestion:
post the ENTIRE original project file (RSS extension) as an attachment to this thread ... (you'll have to zip it first - forum rule) ...
we should be able to help you convert it once we see how it was originally functioning in the RSLogix 500 system ...
So, The LFU is as Ron described.
The ADD is adding the offset value(S:24) + 50 and storing the result in N7:111
And then the CLR is clearing N7:[N7:111]
So, With S:24 set to 0 as it is in the program file, It adds 50 to 0, Sets N7:111 to 50 and clears N7:50.
Now, I don't see anything else in this program that sets S:24.. Is there an HMI/SCADA or another PLC talking to this one?
The LFL and LFU combo is creating a stack of something. Rung 6 adds to the stack and rung 16 removes from the stack.
S:24 is being used to change what stack 'number' is getting loaded/unloaded from, and looking at the instruction comments, I suspect N7:50-59 are the possible different stacks.
So, you'll have to check if there is a tag writing to S:24 in the HMI. That will need to be changed to something else as that register doesn't exist.
You can use array tags here instead and still do indirect addressing that way.
Hello We are looking at upgrading some equipment. At present this equipment uses a AB PLC5 and panelview 1400. We have been back to the...
3,387
I wish to replace an SLC 500 which uses an 1746-N04V Analogue o/p card. As I understand these cards are 14bit D-A. I looking for recommendations...
3,148
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
259
can the slc500 5/05 send a email and text over Ethernet ?
187
Hello, did anybody know, if there exist an converting cable like the1492-CM1746-M01 (for an 1746-IB16 to an 5069-IB16), for an 1746-HSCE to an...
391