slc500 to rlc epax0600
lacruth
Jul 2008
mexicali
41
Hello everybody!!
I have an application with a slc 5/03 and I need to send some information to a large display rlc Epax0600(it has a slave card inside for rs232 com. paxcdc20, and mpaxio20).
The display coms. setup is:
protocol modbus asii, baud 1200, par. odd, data 7, address 7
and plc is:
ch0 mode user, driver ascii, baud 1200, par odd,data 7
cable db9 female from plc pin3(rx) pin12display(tx),pin2(tx) to pin 13(rx) and pin5 com to pin 14 display com.
I tried to use instruction AWA I have not seen error in plc's instruction, but I can't see nothing in display.
Do someone have any experience with these devices?
Is there another instruction I could to use to write the inf. I have in ST17:0 to the display ?
thanks!!
Are you certain the display is set for "Modbus ASCII", rather than simply "ASCII" ?
My understanding of the MPAXIO20 serial slave mode is that it accepts simple ASCII strings.
Post the exact contents of your ST17:0 string, or post the whole *.RSS program.
The AWA or AWT instructions are the correct instructions for this purpose, but we need to see exactly what configuration and data you are using before we can tell you what is correct.
ch0 slc config.
[/ATTACH]
the display has not type simple ascii , options
we have are "modbus ascii and modbus rtu, So I choose modbus ascii.
I've attach the test file I did[/ATTACH]
I'm reading the MPAXI020 "personality module" user manual.
http://www.redlion.net/Products/Groups/Batch/PAXI/Docs/02022.pdf
Page 23 describes the options for serial communications, including "Mbrtu", "MbASC", and "rlc".
The "rlc" method is for the Red Lion ASCII protocol.
If your SLC-5/03 controller has firmware 10 or 11, you could use Modbus RTU protocol natively on the serial port.
Modbus ASCII protocol is very difficult to do with the SLC controller, because you would have to manually calculate the CRC value.
I got it, thanks
and you are right I have rlc type and I put counter C slave mode and it is working fine now.
Thanks again!!
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
280
can the slc500 5/05 send a email and text over Ethernet ?
191
Hello, did anybody know, if there exist an converting cable like the1492-CM1746-M01 (for an 1746-IB16 to an 5069-IB16), for an 1746-HSCE to an...
395
Customer is buying several spare 504 CPU's to have one handy when there's an issue with the ones in operation. Having them on the shelf for years...
2,853
You have to go offline to create the 'Trend' but do you have to download the program to go back Online with the Trend ?