Smc flex

greggerrior

Member
Join Date
Sep 2015
Location
nova scotia
Posts
9
Hey guys
We have an smc flex that faulted. Fault 14. Went through the troubleshooting guide ended up swapping the connections on the back of the controller to see if the fault rolled with the phase change when starting the circuit we had another smc flex fault with the same code just another phase. Tried starting again no fault on the second drive but the first drive faulted again different phase. We are thinking maybe incoming power our voltage hit as low as 290v when starting up on one phase. Any suggestions on where to go from here?
 
Update

Ended up the contacts on one of the phases was welded closed our other soft start is about to do the same didn’t have a spare ended up cleaning up the contact ran fine all night.
 

Similar Topics

I need to purchase a few Large soft starters for our plant and we prefer to stay Rockwell. We have purchased SMC Flex 150 in the past and they...
Replies
7
Views
197
Hi, I want to start 150 SMC Flex from Studio 5000. I have the AOP and P SMC flex AOI imported in my program. I have also set the logic mask to...
Replies
0
Views
331
Hi there, very much new to AB Drives / Drives in general. Driving a pump with SMC Flex Drive Rating: Pump (5-135) Revision 6.008. Currently the...
Replies
6
Views
2,170
Dear experts, I have encountered an SMC Flex (361A,480V) wired for 3-wire where that if you press 'Start' Then immediatly press 'stop' it will...
Replies
7
Views
1,782
Hi, AB Soft Start question, I have (4) SMC Flex 150-F251NBDD controlling 200 hp chip head motors in a sawmill. I am trying to tune the braking...
Replies
0
Views
868
Back
Top Bottom