Solid Red Fault on a CompactLogix 1769-L35e
geniusintraining
Jun 2005
SC
8,277
I was told by the user manual and by users that if you have a solid red fault light then the CPU is shot and it needs to be repaired
I bought a L35e and was flashing it up to V19, a few minutes into the flash it faulted, see below for the code from the flash.
Code:
03/01/13 10:02:27 [-------] User must install FactoryTalk AssetCentre Client 2.31 or above if attempting to log message to FactoryTalk AssetCentre Server.
03/01/13 10:02:39 [SUCCESS] Load Driver: C:\Program Files\Common Files\Rockwell\AB_ASA.DLL
03/01/13 10:02:39 [SUCCESS] Initialize Driver: C:\Program Files\Common Files\Rockwell\AB_ASA.DLL
03/01/13 10:02:48 [SUCCESS] Device Identity: Path = RSLinx API!AB_ETHIP-1 16 12 49 57 50 46 49 54 56 46 48 46 52 52 1 0, Instance = 1,
VID=0x0001, PT=0x000E, PC=0x0041, Maj Rev=15, Min Rev=04, SN=0x003FD517
03/01/13 10:02:48 [FAILURE] Device Identity: Error #10003: GetAttributesAll to Device object - target returned fault status.
  Status: 0x3550
03/01/13 10:03:00 [SUCCESS] Validate:
03/01/13 10:03:00 [SUCCESS] Authorization: Bypass cookie used.
Key: PN-86085
03/01/13 10:03:02 [SUCCESS] Load Script: C:\Program Files\ControlFLASH\0001\000E\0041\PN-86085.nvs
03/01/13 10:03:02 [SUCCESS] Program: Catalog Number = 1769-L35E/A R15.31, Serial Number = 003FD517, Num Updates = 3, Size = 5962544 byte(s).
03/01/13 10:03:04 [SUCCESS] Update: Instance = 3, Size = 2554872 byte(s), Chunk Size = 128 byte(s), Major Rev = 15, Minor Rev = 4
03/01/13 10:03:56 [FAILURE] Transfer: Error #11006: Service cannot be performed while object is in current state.
  GS=0x0C, ES=0x3002
03/01/13 10:05:54 [FAILURE] Transfer: File = C:\Program Files\ControlFLASH\0001\000E\0041\PN-86072.bin, Block = 5724.
So I restarted the CPU and got the solid red fault, so I removed the battery and shorted the positive to the negative for a few minutes (this takes about 10 min) tried short time but it did not help
This is the 3rd solid red light that it has cleared, I don't think it will work for all solid red faults I think the solid red comes from not doing a full boot cycle so I am sure there are several reasons this may happen, I think this one was just at a bad spot in the boot cycle and could not start from the beginning until the capacitors were drained and then it would start over, the other two I received they were red (not flashing) from the start so not sure what happened to them when they faulted in the first place,they were also L32e's.
Just thought I would pass on the info and may save some people a few bucks or some time, I don't think Rockwell recommends this as a practice but if you have a faulted/failed CPU you need to try something and this may work
The second flash to this CPU went great! :)
I have an Schneider M1E 171CBU98090 Processor adapter with only a solid red 'ERR' light lit. Manual explains flashing red ERR but not Solid with...
1,016
Hello, I have a processor module that has a solid Red OK light. Status stuck on WAIT. I have tried the steps to clear memory/restore to...
1,494
Hello I am new to PLCS.net, I have a question here in regards to the Network Status light being solid red on the 1734-AENT. I checked the manual...
1,737
I bought a used L55M23 processor on Ebay and turns out that it doesn't work. RSLinx can't find it whether by RS232 or Ethernet adapter. With this...
3,481
Kindly, we have the following module with its Module Status led solid red. What can we do to solve this? " POINT I/O EtherNet/IP Adapter Module ...
3,989