SPDT Relay Controlling Fwd/Rev Solenoids
JackPW
Feb 2018
East
If I have my PLC output driving a SPDT relay, is there any downside for that relay to control both directional solenoids on a hydraulic valve connected to a cylinder?
Specifically, could the immediate switching have detrimental effects on the relay, solenoid, or valve? should I use one relay for each solenoid with a short delay between? if so, why?
I could use a single solenoid with a spring return but I'm working with existing config.
Thanks in advance
Dont see any reason why not, no need for a delay unless your syatem needs it for process reasons. Bare in mind, using 1 spdt for both valve directions would mean loss of power to the relay because of control issue or estop press would cause the cylinder possibly to move when not desired. Usually what i see is spring centered directional valve and 2 separate relays.
First and foremost.
1. what is the application and what does that cylinder do?
2. if you loose power to the relay and the hydraulics keep running, what will happen when the relay causes the valve to shift?
3. what does your risk assessment tell you?
you MUST ask what if questions. if you cannot answer the question, you MUST find the answer!
in my opinion, you have asked a question without giving a lot of required details. there are too many unknows.
james
Thank you for the reply. I am only interested in any mechanical or electrical degradation associated with this configuration. The process is assumed to be correct
one down side is that one of the solenoids will be energizes all the time it could over heat the solenoid if you have the I/O would use 2 outputs with a relay on each
Power off the solenoid closes cylinder stops all motion
Greetings, Can a Single Pole Double Throw snap switch be furnished such that it actuates on low level or high level, but remains in "neutral"...
2,945
Going to have relays starting/stopping pumps and opening/closing valves. Can i use SPST relays and if not, why?
4,414
Dear, i received a submittal showing motorized valve with SPST instead of SPDT which is required. supplier is unable to comply. what is the real...
4,076
Hi looking to install a smaller less sophisticated PLC for fountain timing and also one analog pressure sensor which would be used to detect...
23
628
Hey guys, I just wanted to see if any of the bright minds on here had any opinions on these relay interface modules. Particularly, I would love to...
78