Specific Energy
YoungWint
Dec 2012
East Midlands
77
If I want to find the specific energy of a pump would I be right in assuming the following, what I want is to get specific energy in kw/m3.
Take the instantaneous motor kW and divide it by the flow rate at flowmeter (this is m3 converted from l/s (x3.6))
This then give me a figure! The problem now is that the instantaneous figure is quite low and I require an integer to sent to other system. What I was thinking was to also accumulate this figure on a one second pulse as I believe the external system can handle this and look for a value change.
Does this seem reasonable? Any other ideas?
Many Thanks
What are you trying to accomplish with this calculation? Note that the value you get is valid at only one head (discharge pressure.)
I've done something like this for pumps in the past, but swapped it around to ls / kw. I was more interested in pump efficiency over time (looking for a performance degradation...), and / or finding the sweet spot in variable speed applications.
Can you add a couple of dp in the PLC, and scale back in the "other system" to make the numbers work??
Hope you are doing well. Currently, I am involed in a revamping project. It requires to stop a mixer at specific postion. For the detail, this...
259
Hello, We recently upgraded our control server to a newer model. After the transition we are experiencing issues with our trend graphs to where...
141
Hi. This is pretty basic but I'm struggling to find an efficient solution. I have a float value of let say 666.555 that I want to move / split...
225
I need to dust off RSNetworks DeviceNet next week for a customer, which means I need to get it loaded on my new laptop. I see my old laptop was...
887
Context: PLC= S7-1212C, HMI=KTP1200 Basic. Hi again, When the "REPORT" button is pressed (on a different screen), it takes the operator to the...
690