Spirax Control Valve issue

Luke_Mages

Member
Join Date
Jun 2014
Location
Buffalo, NY
Posts
117
I know this is a PLC site but it seems that many of you here have been in the industry a lot longer than I.

We have a pneumatically controlled 3" 1/4 spirax valve with a spirax bva200 series controller as the main supply control for 60psi steam. We've ruled out venting being an issue, but the valve doesn't close properly. We swapped out the vlave for a new one and it worked well for about a week and a half and then the same issue started again. We then swapped the pneumatic controller and the same result......

Any ideas?

 
You will need to break the problem down. Is your controller giving a fully closed signal? if yes then it would point to a mechanical issue in the valve if no then you will need to find out why the controller is not giving a full closed output when it should.

If the controller is not giving a full close output when it should then verify and possibly check calibration of it's input (PSI Sensor) and go from there.

Sound like it's just been parts swapping and not trouble shooting thus far.
 
Is the valve rated for steam and the pressure you are operating at? The valve seals / bearings may be swelling or sticking.

what chemical(s) is in the steam?
is there any compressed air involved with the steam flow?

chemicals in the steam or in compressed air may be causing the valve to gum up, seals to swell or dissolve, bearings to become compromised and freeze up.

we had to replace about a 100 valves when a company got in a new air compressor and the compressor oil in the air lines caused the valves to quit working.

a food processing plant I worked for had a similar issue with chemicals.

regards,
james
 
So our distributor and spirax believe its a sizing issue. The customer had spec'd us 100psi when in fact we are at only 50 psi. This is increasing steam velocities to the point that they are damaging the valves and preventing them from properly functioning.
 
So our distributor and spirax believe its a sizing issue. The customer had spec'd us 100psi when in fact we are at only 50 psi. This is increasing steam velocities to the point that they are damaging the valves and preventing them from properly functioning.

I would find that theory a little difficult to swallow. I could not see the valve size be that much of difference on steam velocity. Sound like steam and mirrors.
 
I would find that theory a little difficult to swallow. I could not see the valve size be that much of difference on steam velocity. Sound like steam and mirrors.

we thought the same thing until getting that answer from three different sources and seeing the damage being done to the valve.
 
I've learned a ton from this....what a headache. All I did was write the program to control the system but somehow became the point man for running down this issue.

Of course you did......you wrote the program right?


If your place is anything like mine, you own that puppy until it works perfectly.

Dave
 
And any other time it breaks and the problem is not Obvious or the Mechanic can's find it after 10 Minutes.

Your mechanics give it 10 minutes? You're lucky, mine will dig the hole deeper for a good half hour before turning over the original problem, and 3 more created during "troubleshooting", to me.

Dave
 

Similar Topics

Hey there guys, I'm relatively new to PLC programming. I had a few basic classes in college but since then I have mainly been on the instrument...
Replies
2
Views
141
Hi, Is Control Expert V15.0 supposed to support multiple monitors? I'm running Control Expert V15.0 on my host Windows 11 PC, connected to two...
Replies
1
Views
67
Hello everybody, I'm currently working on a project where I need to implement an IoT platform based on Microsoft Azure Cloud. Communication is...
Replies
2
Views
72
I’m attempt to establish a communication between two simulator M580 CPUs, using a READ_VAR, I have two vitalization Windows 10 in VMWare and each...
Replies
4
Views
148
Adding ethernet equipment to an existing panel that has none. We have some solid ethernet cables coming from other remote cabinets that I plan to...
Replies
3
Views
148
Back
Top Bottom