a dummy way to do this is create an AOI with 10 boolean input, and 1 int output:
in the AOI,
1) convert all 10 bool input to int using mov function (bool to int)
2) after conversion, bit 0 mul by 1, bit 1 mul by 2, bit 2 mul by 4......bit 9 mul by 512
3) sum all the result together and pass to int output
you can then map your bit 0-1, or bit 3-12 on the AOI, example if the AOI input bit0 and 1 both on, 1x1 + 1x2 you will get int value of 3, lets say if AOI all input is on, you will get 1x1 + 1x2 + 1x4 +......1x512 = 1024
Hope this help
There are no AOIs in a 1400, but you could shoehorn in something similar to one and make it nice and ugly and confusing.
I would do the brute force method JaxGTO described, but I am a brute force kind of guy. No need to get cute just for sake of "elegance".
Just use a BFH, and nail the bits where you want them, one by one with much greater efficiency that anything with a loop.
Even that loop approach was fuglier than I'd hoped for, and on top of that in a 1400 each "caller" would need to move things in and out of the N255 file "arguments," etc.
So yah, I agree, no point trying to put lipstick on the pig.
That said, for bit ranges that don't touch the sign bit e.g. ten bits 3-12:
AND srcint 8184 dstint
DIV dstint 8 dstint
Cleaner than brute force XIC/OTE; possibly faster per scan but not enough to matter (lose ~1.5μs on instructions; gain maybe 4-8μs for fewer rungs).
Here is a simple one, just and & shift.
Note: the way this works with the shift is it works on the same variable so the AND function for the bits 3-12 the result is shown as the result of the shift it's just the way it works, rather than shift & store it into another variable it works on the source variable.
Rung 1 just masks bits 0-1
Rung 2 masks the bits 3-12
Rung 3 shifts the 3-12 to 0-9
Any one know how to take a floating point number and convert it so that it can be split to span 2 16-bit words in the +/- 0x7fffffff hex format...
18
5,309
I am close to wits end and would appreciate any new perspective. Cannot go into minutia, but here is a rough rundown of the system and issue we...
26
9,273
Would it be wise / safe to split a 24vdc input from a switch to a PLC and relay? I currently have 14 of the same type of equipment that each have...
1,534
Any one know of way to split a 4-20 mA signal 4 ways? Do they even make such a device? Thanks
3,638
I have an application where I need a single SSI encoder to connect to both a safety controller (SICK Flexi Soft) and a general-purpose PLC...
2,100