ST program calling FB with a TON inside it - TON not working help pls
matt_sd
Jan 2007
Australia
96
This is a strange one, I have a simple alarm filter function block done in Structured Text (ST). I am calling it from a program. When this program is in Ladder it works OK but when the calling program is in Structured Text (ST), the TON timer inside the FB it calls doesn't time. Very strange. My code must have a bug in it but I have use FB calls like this elsewhere and worked ok.
This is programmed with Beckhoff Twincat but any IEC1131 should be the same.
This is alarm filter Function Block:-
FUNCTION_BLOCK alarm_filter_FB
VAR_INPUT
enable:BOOL; (*Enable this FB *)
Inhibit:BOOL; (*This is the inhibit input 1 = Inhibit Alarm*)
alm_in:BOOL; (*This is the Alarm in 1 = Alarm State*)
delay:TIME:=t#5s; (*This is the Delay in seconds (5 seconds is default)*)
END_VAR
VAR_OUTPUT
Alm_out:BOOL; (*This is the alarm output*)
END_VAR
VAR
TON: TON; (* Call TON standard block *)
END_VAR
(* If the inhibit is not set, when the alam input is set, after x time the alarm is generated *)
ton.PT:=delay;
IF NOT Inhibit AND alm_in AND enable THEN
ton.IN:=1;
ELSE
ton.IN:=0;
END_IF
Alm_out:=ton.Q;
THIS IS THE PROGRAM IN ST THAT CALLS THE FB:-
PROGRAM alarm_filter_instance
VAR
input: BOOL;
instance1: alarm_filter_FB;
output: BOOL;
END_VAR
(* Tank Level Low *)
instance1.Delay:=t#10s;
instance1.enable:=1;
instance1.Inhibit:=0;
instance1.Alm_in:= input;
output:=instance1.Alm_out;
If you look at the attached, this is the instance open, the timer is not timing and neither is the delay of 10s been moved into the PT?
Any help appreciated
Matt
I haven't done any Beckhoff programming for some time, but I can't see a call to the function block - your code just writes the input parameters and reads the output parameters.
You didn't call SFB TON, it should be called cyclically from your code for example:
ton(IN:= alm_in AND enable AND NOT inhibit,
PT:= delay);
Alm_out:= ton.Q;
Thank gregoryg & L D[AR2,P#0.0].
That seems like the problem. I have programmed ladder for 15 years but only programmed in ST in the last 6 months.
I thought that as TON was declared, it would be called (just like ladder)
ST is good in Beckhoff as there are not the modules created in ladder (unlike Control logix where all the modules exist in ladder)
Thanks again, you have saved me time :)
Regards
Matt
member.php?u=21496
I have mapped data tags Vlt_1 and Amp_1 from a device_1 (with ip address) to a red lion programmable controller which is connected to it over...
1,406
Hi, i am using DVP-14SS2 PLC, after program written to plc, when power is reset, plc doesn't run. always need to connect to pc for the run mode.
Hi all, hope you are having a great day, I am in need of your help to create a AOI or program that does this kind of job: I have a IO Link...
23
352
Hi. I have a 222 CPU. I need to recover the program from the eeprom memory. Is it possible?
97
Can we use a Simotion D455 ethernet port x127 as a gate, to access S7-1500 plc Tia Portal program ? In the Simatic manager, we used Netpro to do...
89