Star-Delta Starter
star (wye) delta starting
goody
thought youre explaination was pretty good in laymans terms. :)
I also am an electrical engineer from the uk and am appalled at the number of "experienced :( " electricians that do not know how to connect a star/delta motor up.
DickDV you are also right But goody ive got to agree with you its star/delta although you can see the wye (although i have heard of it b4)
Just to clairify i am in the US and using 480v 3 phase. the starter in question is OEM standard Seimems using 3 contactors. The three are directly next to each other the right most starter has what looks like a premanufatured insulated 3 pole jumper on the line side, it looks like each phase is shorted?? This contactor is connected on the load side to the one directly to its left with again a premanufactured jumper much like on a reversing starter, it also has leads going directly to the motor. the left most contactor is also feeding the motor on the delta connection.
Wye/Star
I would like to point out to you English chaps that an induction
motor and bulk of the AC current devices were invented right here in
USA by Nikola Tesla. Therefore I submit to you that the American
coined terminology should be used even in England! Just kidding.
Yes, you blokes always have to be different.
One more thing on the subject of Wye - Delta motors.
They could be very difficult to protect in some applications.
That's because of the disparity between Wye (STARRRR) and Delta load currents coupled with possibility of having varying load.
I had such situation on a European designed grinder (50 HP motor).
After burning up the motor several times I ended up replacing
the manufacturer supplied protection overloads. That didn't help.
We ended up junking the motor and using a standard 3 phase
induction motor with solid state protective devices. It worked like a charm.
P.S.
It's the hood not a bonnet
It's the trunk not a boot.
It's the elevator not a lift.
AND IT'S the WYE not a Star.
Jingoism
You forgot to blurt on about which side of the road is the right side.
Are you suggesting that if the device in question was labelled 'Y-Delta', SLaubach never would have had to ask the question? He claims to be from Pennsylvania and last time I checked that was still in the US of A.
Goody said:
Star Delta, the first time you come across it can be confusing. I have had many calls from experienced electricians that do not know how to connect a star/delta motor up.
For that matter I do not think there is a standard method. It all depends how the wires are connected at the contactors.
Some connect at the contactor end A1 B1 C1 A2 B2 C2 and some connect A1 B1 C1 B2 C2 A2.
Then there is the worst scenario; the 6 winding wires are hanging out of the motor with no markings. (I have had this)
You cannot tell which are 1’s and which are 2’s.
You can find the three windings but you cannot tell which side they should go on..
It is down to trial and error and if you get it wrong, 2 windings are trying to go one way and the third is trying to go the other. The motor makes some great noises and if you are not quick, you let the smoke out.
FYI There is an easy non-destructive way to tell the 1's from the 2's, but it requires the use of a low voltage AC supply (DC won't do!).
If you label the wires as A&A, B&B, C&C, then connect one of the B's to one of the C's
Connect the low voltage supply to the wires A&A
Then check for an induced voltage across the wires B & C that are not joined together. If a voltage is present the you have connected a B1 to a C2 - if not then you have connected a B1 to a C1. A voltage of 10VAC supplied to A&A will give about 4VAC across the B&C wires.
Then use this method again with the A&C wires joined and voltage applied to wires B1 & B2
Hope this all makes sense
An FYI: The star delta method is not an American concept, it orginated in Europe and was in the US for compressors (hvac and air). To maybe clear the air about motor connections and how to determine connections when not marked I have prepared the following. This site limits text so I am dividing this into parts and creating a web page for it. To see it in its entirety and better organized goto MY MOTOR WEBPAGE
Code:
<p align="center"><b><font size="4">Electric Motor Wire Marking & Connections</font></b></p>
<p align="left"><b><font size="3"><span style="background-color: #FFFF00">Single Phase
Connections:</span>
<u>(Three Phase--see below)</u><br>
</font><font size="2">Single
Voltage:                                                       </font></b></p>
<div align="center"><center>
<table border="1" width="20%">
  <tr>
    <td width="33%"><font size="2"><b>Rotation</b></font></td>
    <td width="36%"><font size="2"><b> L1</b></font></td>
    <td width="33%"><font size="2"><b>L2</b></font></td>
  </tr>
  <tr>
    <td width="33%"><font size="2"><b>CCW</b></font></td>
    <td width="36%"><font size="2"><b> 1,8</b></font></td>
    <td width="33%"><font size="2"><b>4,5</b></font></td>
  </tr>
  <tr>
    <td width="33%"><font size="2"><b>CW</b></font></td>
    <td width="36%"><font size="2"><b> 1,5</b></font></td>
    <td width="33%"><font size="2"><b>4,8</b></font></td>
  </tr>
</table>
</center></div>
</font><font size="2">Dual Voltage: (Main Winding Only)</font></b></p>
<table border="1" width="30%">
  <tr>
    <td width="20%"><font size="2"><b>Voltage</b></font></td>
    <td width="20%"><font size="2"><b>Rotation</b></font></td>
    <td width="20%"><font size="2"><b> L1</b></font></td>
    <td width="20%"><font size="2"><b> L2</b></font></td>
    <td width="20%"><font size="2"><b>  Join</b></font></td>
  </tr>
  <tr>
    <td width="20%"><font size="2"><b>High</b></font></td>
    <td width="20%"><font size="2"><b>CCW</b></font></td>
    <td width="20%"><font size="2"><b> 1</b></font></td>
    <td width="20%"><font size="2"><b> 4,5</b></font></td>
    <td width="20%"><font size="2"><b>2&3&8</b></font></td>
  </tr>
  <tr>
    <td width="20%" bgcolor="#C0C0C0" bordercolor="#C0C0C0"> </td>
    <td width="20%"><font size="2"><b>CW</b></font></td>
    <td width="20%"><font size="2"><b> 4,8</b></font></td>
    <td width="20%"><font size="2"><b>2&3&5</b></font></td>
  </tr>
  <tr>
    <td width="20%"><font size="2"><b>Low</b></font></td>
    <td width="20%"><font size="2"><b>1,3,8</b></font></td>
    <td width="20%"><font size="2"><b>2,4,5</b></font></td>
    <td width="20%"><font size="2"><b>  -------</b></font></td>
  </tr>
  <tr>
    <td width="20%"><font size="2"><b>1,3,5</b></font></td>
    <td width="20%"><font size="2"><b>2,4,8</b></font></td>
  </tr>
</table>
</center></div>
<p align="left"><b><font size="4">
</font><font size="2">Dual Voltage: (Main & Auxiliary Winding)</font></b></p>
  <tr>
  </tr>
  <tr>
    <td width="20%"><b>1,8</b></td>
    <td width="20%"><b>4,5</b></td>
    <td width="20%"><b>2&3,6&7</b></td>
  </tr>
  <tr>
    <td width="20%"><b>1,5</b></td>
    <td width="20%"><b>4,8</b></td>
  </tr>
  <tr>
    <td width="20%"><b>1,3,6,8</b></td>
    <td width="20%"><b>2,4,5,7</b></td>
    <td width="20%"><b>  ---------</b></td>
  </tr>
  <tr>
    <td width="20%"><b>1,3,5,7</b></td>
    <td width="20%"><b>2,4,6,8</b></td>
  </tr>
</table>
</center></div>
<p align="left"><b>Single Phase Terminal Markings Identified By Color: <font size="1">(NEMA
Standards)</font><br>
        <font size="2">1-Blue
5-Black
P1-No color assigned<br>
2-White         6-No color
assigned       P2-Brown <br>
3-Orange      7-No color assigned <br>
4-Yellow        8-Red </font></b></p>
Code:
<p align="left"><font size="3"><b><u>Three</u> <u>Phase</u> <u>Connections</u>:</b></font></p>
<p align="left">   <b><font size="2">Part Winding Start:<br>
<u>6 Leads</u>  NEMA Nomenclature:<u><br>
</u>
WYE or Delta Connected</font></b></p>
<table border="1" width="50%">
  <tr>
    <td width="55%" bgcolor="#C0C0C0" bordercolor="#C0C0C0"> </td>
    <td width="14%"><b><font size="3"> T1</font></b></td>
    <td width="14%"><b><font size="3"> T2</font></b></td>
    <td width="15%"><font size="3"><b> T3</b></font></td>
    <td width="13%"><font size="3"><b>T7  </b></font></td>
    <td width="14%"><font size="3"><b> T8  </b></font></td>
    <td width="13%"><font size="3"><b>T9   </b></font></td>
  </tr>
  <tr>
    <td width="55%"><b><font size="3">Motor Leads</font></b></td>
    <td width="14%"><font size="3"><b>  1</b></font></td>
    <td width="14%"><font size="3"><b>  2</b></font></td>
    <td width="15%"><b><font size="3">  3</font></b></td>
    <td width="13%"> <font size="3"><b>7 </b></font></td>
    <td width="14%"><b><font size="3">  8</font></b></td>
    <td width="13%"><b><font size="3">  9</font></b></td>
  </tr>
</table>
</center></div>
<p>   <b><font size="3">
</font><font size="2"><u>9 Leads</u> </font><font size="3"> </font><font size="2">NEMA
Nomenclature   </font><font size="3"> <br>
   </font></b>
<b><font size="2">WYE Connected (low voltage only) </font></b></p>
<table border="1" width="66%">
  <tr>
    <td width="104%" bordercolor="#C0C0C0" bgcolor="#C0C0C0"> </td>
    <td width="12%"><b><font size="3"> T1</font></b></td>
    <td width="12%"><b><font size="3"> T2</font></b></td>
    <td width="13%"><font size="3"><b> T3</b></font></td>
    <td width="13%"><font size="3"><b> T7</b></font></td>
    <td width="12%"><font size="3"><b> T8  </b></font></td>
    <td width="21%"><font size="3"><b> T9</b></font></td>
    <td width="91%"><font size="3"><b>   Together</b></font></td>
  </tr>
  <tr>
    <td width="104%"><b><font size="3">Motor Leads</font></b></td>
    <td width="12%"><font size="3"><b>  1</b></font></td>
    <td width="12%"><font size="3"><b>  2</b></font></td>
    <td width="13%"><b><font size="3">  3</font></b></td>
    <td width="13%">  <b>7</b></td>
    <td width="12%"><b><font size="3">  8</font></b></td>
    <td width="21%"><b><font size="3">  9</font></b></td>
    <td width="91%"><b><font size="3">     4&5&6</font></b></td>
  </tr>
</table>
</center></div>
<p>
<font size="2"><b><u>12 Leads</u>   NEMA & IEC Nomenclature<u><br>
</u>
Single Voltage or Low Voltage of Dual-Voltage Motors</b></font></p>
<table border="1" width="46%">
  <tr>
    <td width="42%" bgcolor="#C0C0C0" bordercolor="#C0C0C0"><p align="left"> </td>
    <td width="16%"><b><font size="3"> T1</font></b></td>
    <td width="18%"><b><font size="3"> T2</font></b></td>
    <td width="17%"><font size="3"><b> T3</b></font></td>
    <td width="16%"><font size="3"><b> T7  </b></font></td>
    <td width="16%"><font size="3"><b> T8  </b></font></td>
  </tr>
  <tr>
    <td width="42%"><font size="3"><b> NEMA</b></font></td>
    <td width="16%"><font size="3"><b> 1,6</b></font></td>
    <td width="18%"><b><font size="3"> 2,4</font></b></td>
    <td width="17%"> <b>3,5</b></td>
    <td width="16%"><b><font size="3">7,12</font></b></td>
    <td width="16%"><b><font size="3">8,10</font></b></td>
    <td width="13%"><b><font size="3">9,11</font></b></td>
  </tr>
  <tr>
    <td width="42%"><b><font size="3">  IEC</font></b></td>
    <td width="16%"><font size="3"><b>  1</b></font></td>
    <td width="18%"><font size="3"><b>  2</b></font></td>
    <td width="17%"><b><font size="3">  3</font></b></td>
    <td width="16%"> <font size="3"><b>7 </b></font></td>
    <td width="16%"><b><font size="3">  8</font></b></td>
  </tr>
</table>
</center></div>
<p><b><font size="3"><span style="background-color: #FFFF00"><u>Three Phase Motors-Single
Speed </u></span></font></b></p>
Nema Nomenclature--6 Leads:<u><br>
<br>
</u>
  </font><font size="2">Single Voltage--External WYE
Connection              </font><font
size="3">   </font></b></p>
<table border="1" width="27%">
  <tr>
    <td width="14%"><font size="3"><b> L1</b></font></td>
    <td width="33%"><font size="3"><b>L2</b></font></td>
    <td width="24%"><b>L3</b></td>
    <td width="88%"><font size="3"><b>  Join</b></font></td>
  </tr>
  <tr>
    <td width="14%">  <b>1 </b></td>
    <td width="33%"><b><font size="3">  2</font></b></td>
    <td width="24%"> <b>3</b></td>
    <td width="88%"><b><font size="3"> 4&5&6</font></b></td>
  </tr>
</table>
</center></div>
<p>   <b><font size="3">                        </font><font
size="2">Single Voltage--External Delta Connection</font></b></p>
<table border="1" width="15%">
  <tr>
    <td width="33%"><b>L1</b></td>
    <td width="24%"><b>L2</b></td>
    <td width="44%"><b>L3</b></td>
  </tr>
  <tr>
    <td width="33%"><font size="3"><b>1,6</b></font></td>
    <td width="24%"><font size="3"><b>2,4</b></font></td>
    <td width="44%"><font size="3"><b>3,5</b></font></td>
  </tr>
</table>
</center></div>
</font><font size="2">Single Voltage WYE-Delta Connections</font></b></p>
<table border="1" width="55%">
  <tr>
    <td width="41%"><b><font size="2">Operating mode</font></b></td>
    <th width="20%"><font size="2"><b>Connection</b></font></th>
    <td width="14%"><b> L1</b></td>
    <td width="17%"><b> L2 </b></td>
    <td width="15%"><b> L3</b></td>
    <td width="17%"><b>Join</b></td>
  </tr>
  <tr>
    <td width="41%"><font size="3"><b>    Start</b></font></td>
    <td width="20%"><b>  WYE</b></td>
    <td width="14%"><b>   1</b></td>
    <td width="17%"><b>  2</b></td>
    <td width="15%"><b>  3   </b></td>
    <td width="17%"><b>4&5&6</b></td>
  </tr>
  <tr>
    <td width="41%"><b>    Run</b></td>
    <td width="20%"><b>  Delta</b></td>
    <td width="14%"><b> 1,6</b></td>
    <td width="17%"><b> 2,4</b></td>
    <td width="15%"><b> 3,5</b></td>
    <td width="17%"><b>  -------</b></td>
  </tr>
</table>
</center></div>
Code:
<p>   <b>
<font size="2">Dual Voltage WYE-Delta Connections</font></b></p>
  <tr>
    <td width="41%"><b><font size="2">     Voltage</font></b></td>
  </tr>
  <tr>
    <td width="41%"><font size="3"><b>     High  </b></font></td>
  </tr>
  <tr>
    <td width="41%"><b>     Low</b></td>
  </tr>
</table>
</center></div>
<p>   <b>
NEMA Nomenclature--9 Leads:<br>
<font size="2">Dual Voltage WYE-Connected  </font></b></p>
<table border="1" width="48%">
  <tr>
    <td width="20%"><b><font size="2">Voltage</font></b></td>
    <td width="14%"><b> L2</b></td>
    <td width="13%"><b> L3</b></td>
    <td width="42%"><b>      Join</b></td>
  </tr>
  <tr>
    <td width="20%"><b> <font size="3">High</font></b></td>
    <td width="14%"><b>   2   </b></td>
    <td width="13%"><b>   3</b></td>
    <td width="42%"><b> 4&7, 5&8, 6&9</b></td>
  </tr>
  <tr>
    <td width="20%"><b> Low</b></td>
    <td width="14%"><b> 1,7</b></td>
    <td width="14%"><b> 2,8</b></td>
    <td width="13%"><b> 3,9</b></td>
    <td width="42%"><b>    4&5&6</b></td>
  </tr>
</table>
</center></div>
<p><b>
<font size="2">Dual Voltage Delta-Connected</font></b></p>
<table border="1" width="52%">
  <tr>
    <td width="16%"><b>   L2</b></td>
    <td width="17%"><b>  L3</b></td>
    <td width="36%"><b>      Join</b></td>
  </tr>
  <tr>
    <td width="16%"><b>    2   </b></td>
    <td width="17%"><b>   3</b></td>
    <td width="36%"><b>4&7, 5&8,6&9</b></td>
  </tr>
  <tr>
    <td width="14%"><b>1,6,7</b></td>
    <td width="16%"><b>2,4,8</b></td>
    <td width="17%"><b> 3,5,9</b></td>
    <td width="36%"><b>    ------------</b></td>
  </tr>
</table>
</center></div>
<p>   <b>
NEMA Nomenclature--12 Leads:<br>
<font size="2">Dual Voltage--External WYE Connection</font></b></p>
<table border="1" width="65%">
  <tr>
    <td width="9%"><b> L1</b></td>
    <td width="9%"><b>L2</b></td>
    <td width="12%"><b>  L3</b></td>
    <td width="53%"><b>      Join</b></td>
  </tr>
  <tr>
    <td width="9%"><b>   1</b></td>
    <td width="9%"><b>  2 </b></td>
    <td width="12%"><b>   3</b></td>
    <td width="53%"><b>4&7, 5&8, 6&9, 10&11&12</b></td>
  </tr>
  <tr>
    <td width="9%"><b>1,7  </b></td>
    <td width="9%"><b> 2,8</b></td>
    <td width="12%"><b>  3,9</b></td>
    <td width="53%"><b>4&5&6,  10&11&12</b></td>
  </tr>
</table>
</center></div>
Code:
<p>   <b>
<font size="2">Dual Voltage<br>
WYE-Connected Start<br>
Delta-Connected Run  </font></b></p>
<table border="1" width="62%">
  <tr>
    <td width="20%"><b>Voltage</b></td>
    <td width="17%"><b>Conn.</b></td>
    <td width="12%"><b> L1</b></td>
  </tr>
  <tr>
    <td width="20%"><b>High</b></td>
    <td width="17%"><b> WYE</b></td>
    <td width="12%"><b>   1</b></td>
    <td width="9%"><b>  2</b></td>
  </tr>
  <tr>
    <td width="17%"><b>Delta</b></td>
    <td width="12%"><b>  1,12</b></td>
    <td width="9%"><b>  2,10</b></td>
    <td width="12%"><b>   3,11</b></td>
    <td width="53%"><b>4&7, 5&8, 6&9</b></td>
  </tr>
  <tr>
    <td width="20%"><b>Low</b></td>
    <td width="12%"><b>   1,7</b></td>
  </tr>
  <tr>
    <td width="12%"><b>1,6,7,12</b></td>
    <td width="9%"><b>2,4,8,10</b></td>
    <td width="12%"><b>3,5,9,11</b></td>
    <td width="53%"><b>   ------------</b></td>
  </tr>
</table>
</center></div>
<p>            <b><font size="3">IEC
Nomenclature--6 & 12 Leads:<br>
</font><font size="2">Single Voltage WYE-Delta Connections</font><font size="3">                        </font>
<font size="2">Single Voltage WYE-Delta Connections</font><font size="3">                        </font></b></p>
<table border="1" width="53%">
  <tr>
    <td width="20%"><b>oper-<br>
    mode</b></td>
    <td width="14%"><b>Conn.</b></td>
    <td width="18%"><b> L1</b></td>
    <td width="17%"><b> L2</b></td>
    <td width="20%"><b> L3</b></td>
  </tr>
  <tr>
    <td width="20%"><b>Start</b></td>
    <td width="14%"><b> WYE</b></td>
    <td width="18%"><b>  U1</b></td>
    <td width="17%"><b> V1 </b></td>
    <td width="20%"><b> W1</b></td>
    <td width="42%"><b>U2&V2&W2 </b></td>
  </tr>
  <tr>
    <td width="20%"><b>Run</b></td>
    <td width="14%"><b>Delta</b></td>
    <td width="18%"><b>U1,W2</b></td>
    <td width="17%"><b>V1,U2</b></td>
    <td width="20%"><b>W1,V2</b></td>
    <td width="42%"><b>   --------------</b></td>
  </tr>
</table>
</center></div>
<p>   <b>
Dual Voltage WYE-Delta Connections</b></p>
  <tr>
    <td width="20%"><b>Volt</b></td>
  </tr>
  <tr>
    <td width="18%"><b>  U 1</b></td>
  </tr>
  <tr>
    <td width="20%"><b>Low   </b></td>
  </tr>
</table>
</center></div>
<p>   <b>
Dual Voltage WYE-Connected Start<br>
Delta-Connected Run</b></p>
<table border="1" width="38%">
  <tr>
  </tr>
  <tr>
    <td width="42%"><b>U2&U5,V2&V5, W2&W5,U6&V6&W6</b></td>
  </tr>
  <tr>
    <td width="18%"><b>U1,W6</b></td>
    <td width="17%"><b>V1,U6</b></td>
    <td width="20%"><b>W1,V6</b></td>
    <td width="42%"><b>U2&U5,V2&V5,<br>
    W2&W6</b></td>
  </tr>
  <tr>
    <td width="20%"><b>LOW</b></td>
    <td width="14%"><b>WYE</b></td>
    <td width="18%"><b>U1,U5</b></td>
    <td width="17%"><b>V1,V5</b></td>
    <td width="20%"><b>W1,W5</b></td>
    <td width="42%"><b>U2&V2&W2,<br>
    U6&V6&W6</b></td>
  </tr>
  <tr>
    <td width="18%"><b>U1,U5,<br>
    W2,W6</b></td>
    <td width="17%"><b>V1,V5<br>
    U2,U6</b></td>
    <td width="20%"><b>W1,W5<br>
    V2,V6</b></td>
    <td width="42%"><b>   -----------------------------</b></td>
  </tr>
</table>
</center></div>
<p>   <b>         <font size="3">NEMA
Nomenclature--6 Leads: <br>
</font><font size="2">Constant Torque Connection </font></b><font size="1">(Low-speed HP
is half of high-speed HP)</font></p>
  <tr>
    <td width="20%"><b><font size="2">Speed</font></b></td>
    <td width="11%"><b>L1</b></td>
    <td width="11%"><b>L2</b></td>
    <td width="11%"><b>L3</b></td>
    <td width="45%" bgcolor="#C0C0C0" bordercolor="#C0C0C0"> </td>
    <td width="55%"><b><font size="2">Typical <br>
    Connection</font>    </b></td>
  </tr>
  <tr>
    <td width="11%"> <b> 6</b></td>
    <td width="11%"><b>  4 </b></td>
    <td width="11%"><b>  5</b></td>
    <td width="45%"><b>1&2&3Join</b></td>
    <td width="55%"><b>2 WYE</b></td>
  </tr>
  <tr>
    <td width="11%"><b>  1</b></td>
    <td width="11%"><b>  2 </b></td>
    <td width="11%"><b>  3</b></td>
    <td width="45%"><b> 4-5-6 Open</b></td>
    <td width="55%"><b>1 Delta  </b></td>
  </tr>
</table>
</center></div>
Code:
<p>   <b>            <font
size="2">
Variable Torque Connection </font><font size="1"> </b>(Low-speed HP is 1/4 of
  <tr>
  </tr>
  <tr>
  </tr>
  <tr>
    <td width="55%"><b>1 WYE</b></td>
  </tr>
</table>
</center></div>
<p>   <b>
<font size="2">Constant Horsepower Connection </font></b><font size="1">(HP is the same at
both speeds)</font></p>
  <tr>
    <td width="52%" bgcolor="#C0C0C0" bordercolor="#C0C0C0"> </td>
    <td width="49%"><b><font size="2">Typical <br>
  </tr>
  <tr>
    <td width="52%"><b>1-2-3 Open</b></td>
    <td width="49%"><b>1 Delta</b></td>
  </tr>
  <tr>
    <td width="52%"><b>4&5&6<font color="#FFFFFF">-</font>Join</b></td>
    <td width="49%"><b>2 WYE</b></td>
  </tr>
</table>
</center></div>
<p>
<b>IEC Nomenclature--6 Leads: </b>  <font size="2"><b>        <br>
Constant Torque
Connection                       </b></font></p>
  <tr>
    <td width="85%" bgcolor="#C0C0C0" bordercolor="#C0C0C0"> </td>
    <td width="44%"><b><font size="2">Typical <br>
  </tr>
  <tr>
    <td width="11%"><b>2W</b></td>
    <td width="11%"><b>2U</b></td>
    <td width="11%"><b>2V</b></td>
    <td width="85%"><b>1U&1V&1W<font color="#FFFFFF">--</font>JOIN</b></td>
    <td width="44%"><b>2 WYE</b></td>
  </tr>
  <tr>
    <td width="11%"><b>1U</b></td>
    <td width="11%"><b>1V</b></td>
    <td width="11%"><b>1W</b></td>
    <td width="85%"><b>2U-2V-2W  OPEN</b></td>
    <td width="44%"><b>1 Delta</b></td>
  </tr>
</table>
</center></div>
<p>   <font size="2"><b>
Variable Torque Connection</b></font></p>
  <tr>
  </tr>
  <tr>
    <td width="85%"><b>1U&1V&1W<font color="#C0C0C0">--</font>JOIN</b></td>
  </tr>
  <tr>
    <td width="44%"><b>1 WYE</b></td>
  </tr>
</table>
</center></div>
<p align="left" class="headers2"><strong>Identifying Leads of a Nine Lead Three Phase
Motor </strong></p>
<i><b>
<p align="justify"></b></i>For the purpose of this project, a lantern battery of six or
nine volts works best. Use a DC volt-ohm meter with a 20K ohms per volt DC scale. Battery
and voltmeter leads should be properly identified. Alligator clips should be used on both.
The motor must be completely assembled. Test the nine leads for continuity with the
ohmmeter to determine whether the motor is star (wye) or delta connected. The delta
connected motor will possess three sets of three leads with continuity between them. On
the other hand, the star connected motor will have only one set of three leads with
continuity between them, and three sets of two leads with continuity. Following are
specific steps to take when identifying leads of both a star connected and a delta
connected motor. Refer to the diagrams on the following page for further details.<b><u></p>
<p align="justify">Delta Connected Motor</u>:</b></p>
<p align="justify">Using an ohmmeter, identify the three groups of three leads. Separate
these groups by tying them with tape. Attach leads to a pair of wires in a group, and
observe the voltage drop from each pair of energized leads to the third lead in that
group. Continue until a combination is found that gives a voltage drop from each of the
energized leads to the third lead equal to one half of the battery voltage. The lead
located halfway between the other two will thus be the corner lead of the delta. Repeat
this for each group of leads, marking the corner leads #1, #2, and #3.</p>
<p align="justify">Next, use the inductive kick test method to identify the proper
markings for the other two leads of each group. The two coils #3 & #6 and #3 & #8,
acting in parallel, will produce the effect of a coil positioned halfway between the
actual position of the two coils. The flux produced by #3 & #6 and #3 & #8
combined, will be perpendicular to the axis of #1 & #4 and #2 & #7. Opening and
closing a switch in this circuit will produce a kick in coils #1 & #9 and #2 & #5,
but no kick in #1 & #4 and #2 & #7.</p>
<p align="justify">Therefore, if the battery is connected from #3 & #6 and #3 & #8
as shown, opening and closing the battery circuit, the voltmeter will identify leads #1,
#4, and #9 and can be distinguished by noting the magnitude rather than the polarity. The
voltmeter can then be connected to terminal #2 for determination of the leads #5 & #7.
Leads #2 to #7 will give little or no deflection, and leads #2 to #5 will give a
substantial deflection.</p>
<p align="justify">In succession, the battery is then transferred to the corner of #1. Tie
the battery between leads #1 & #4 & #9. Making and breaking the circuit will be
perpendicular to #3 & #8 and #2 & #5, resulting in no deflection. However, there
will be a deflection from leads #2 & #7 and #3 & #6. Placing the battery next on
the #2 & #5 and #2 & #7 leads will be perpendicular to #1 & #9 and #3 & #6
leads, therefore creating no deflection. Leads #1 & #4 and #3 & #8 would then have
a deflection, thus concluding the lead testing of the nine lead delta connected motor.<b><u></p>
<p align="justify"><br>
Star Connected Motor</u>:</b></p>
<p align="justify">Mark the three leads with continuity, #7, #8, and #9. Clip the battery
to the #8 & #9 pair, clipping onto one and flashing the other. Clip the voltmeter to
each pair of leads with continuity between them, until a pair is found that produces
little to no "kick" or deflection. This pair of leads consists of the #1 &
#4 leads. Next, move the battery to the #7 & #8 combination, with the positive lead on
the #7 lead and the negative lead to be used for flashing the #8 lead. The voltmeter is so
placed on the #1 & #4 pair that an upscale deflection is observed on the
"make" of the negative #8 lead. The voltmeter positive lead is then the #1 motor
lead, and the negative voltmeter is the #4 motor lead. </p>
<p align="justify">Next, move the battery to #7 & #9 leads with the positive lead on
the #9 motor lead, and the negative to flash the #7 lead. Identification of the #3 motor
lead is then determined by an upscale kick. The positive voltmeter lead should be on this
lead, and the negative lead should be on the #6 motor lead. Shift the battery to the #8
& #9 pair, with the positive battery lead on the #8 lead and the negative used for the
flashing. An upscale kick will identify the #2 motor lead. The positive voltmeter lead
will be found on the #2 lead, and the negative voltmeter lead will be the #5 lead. This
concludes the lead testing of the nine lead star connected motor.</p>
motorlead2.gif.
AC motor starting currents can be up to 3 times the normal run current. This is not an issue with small motors but when you deal with the larger motors with run currents of 25Amps, 50 Amps, 100 Amps or more this can overload the source power line and consequently reduce the voltage on the main line and affect other devices such as computers, etc.
These larger motors can have dual voltage windings normally called High voltage and Low voltage connections. By starting the motor in its high voltage lower current STAR connection and then switching to its low voltage higher current DELTA connection after the motor has started turning will signifigantly reduce the starting current. A typical Star to Delta switching time of one to 3 seconds is all that is required.
Thank you. I be in and out from time to time. I am not a plc guru but alot of topics do surface that I and familiar/good at.
Hi all, Got a customer who's asked me to look at a new machine they've gotten in which they're having trouble starting. It's a brand new...
4,281
Without going into a lot of detail, 150 hp motor with a Star/Delta Start how much time on Star before switching to Delta. This is a compressor, I...
2,020
Star Delta Starter with Timer Relay or with PLC Timer. Any preferences? Any reasons one way or another?
4,441
A dust collector blower fan motor 18kW, previously run by a star-delta starter, has been replaced with a VFD( Brand: LS, Model: SV-iP5A). Our...
38
11,790
Hi every one What is the basis on which a motor star/delta starter is chosen? I mean is it necessary to use star delta with every motor ? and...
5,832