fmichael,
a "typical" AC-motor of the squirrel-cage type has a starting current approx 7 times that of FLA, not 12-16 times. There are exceptions, but as long as we are talking about commercial standard motors, then 7 times is a good rule of thumb.
awalinski,
what does the nameplate of the motor say about power, voltage, current, maybe in various combinations ?
And at what voltage are you intending to use it ?
As some of the others has pointed out, if the motor is 60hp and 103FLA at 380V,
then it will be derated to approx. 20hp and 34FLA at 230V.
But you will have to check with the nameplate.
34FLA will give a starting current of approx. 220A with direct start (now I too know what "across the line" means ). Thats the value that your electrical provider should say OK or NOT OK to, provided that the above assumptions are correct.
You have a number of options to reduce the inrush current,
star-delta, softstarter, transformerstarter, VFD.
Today low cost softstarters are so cheap that they can replace star-delta starters. Low cost softstarters are barebones with the softstarting thyristors in only 2 phases. All the major manufacturers are selling them now, I use some from Siemens.
a "typical" AC-motor of the squirrel-cage type has a starting current approx 7 times that of FLA, not 12-16 times. There are exceptions, but as long as we are talking about commercial standard motors, then 7 times is a good rule of thumb.
awalinski,
what does the nameplate of the motor say about power, voltage, current, maybe in various combinations ?
And at what voltage are you intending to use it ?
As some of the others has pointed out, if the motor is 60hp and 103FLA at 380V,
then it will be derated to approx. 20hp and 34FLA at 230V.
But you will have to check with the nameplate.
34FLA will give a starting current of approx. 220A with direct start (now I too know what "across the line" means ). Thats the value that your electrical provider should say OK or NOT OK to, provided that the above assumptions are correct.
You have a number of options to reduce the inrush current,
star-delta, softstarter, transformerstarter, VFD.
Today low cost softstarters are so cheap that they can replace star-delta starters. Low cost softstarters are barebones with the softstarting thyristors in only 2 phases. All the major manufacturers are selling them now, I use some from Siemens.