Step7 - Can someone tell me what's wrong with this!
RMA
Sep 2004
North of Hamburg, Germany
2,052
This is the simple program I wrote to save the maximum values of some analog signals.
Initially everything seemed to work OK - the carrier tray number, date and time were saved in the first few Bytes of the target DB, but I had forgotten to copy the actual maximum value to the Target DB. I then added the last four lines in NW2 to do this and the CPU promptly went into STOP, complaining that I wasn't accessing a word boundary.
I can't see what's wrong with it - I hope someone else can!
Cheers
Roy
Oops, forgot to rename the file to .txt!
You forgot to attach the code but my guess is you haven't multiplied by (8*no of bytes) to convert to pointer format !
What resets #cntr to zero - is this done outside of this block because when I run it the indirect accesses soon fall off the end of the data block I created (1800 bytes long)
Simon, at this stage I hadn't implemented the reset of Cntr, I now check after loading it in NW1 that it doesn't exceed 511 and the DB has 512 UDT entries. If it does, I reset to zero and overwrite the old data. 512 entries is enough for about 4 hours of production.
10BaseT., I'll post the UDT in a few minutes, that will probably be my last opportunity to post today, though.
Cheers
Roy
If the number of entries will exceed 255 then you want to use the + 1 instruction instead of the INC 1 instruction as the latter only affects the lower 8 bits of the accumulator.
What about the calls to "DT_DATE" and "DT_TOD" are these your blocks or SFC's or what - I've had to comment them out.
just a guess:
L #Pntr; //Get base pointer to Target_DB
LAR1 ; //back into AR1
AUF #Target_DB; //reopen Target DB
L #Analog_Alt; // <-- this line i should add
T DBW [AR1,P#8.0]; //and transfer ...
Polle
Well spotted Polle - this is a coding error that will result in the incorrect data being stored for the max analogue value - however, it does not explain the reported fault of an area write not on a word boundary.
Roy - can you post the exact event id from the diagnostic buffer please.
OK - found FC6 and FC8 for "DT_DATE" and "DT_TOD".
For cases like this I don't load OB121 so the plc stops at the relevant point and you can then open the block at the offending intruction. You can also examine the I Stack to see the contents of the accumulators and address registers at the point of the error. (I almost always do this in the simulator though)
Polle, thanks for that, somehow I had convinced myself the value was still in AKKU1 although I had just loaded the pointer!
Simon, I knew that INC only operated on the byte, but didn't bother to check how many that was, I just guessed it was 512, oops!:oops:
Here is the diagnostic text and the stack. By the way, if you could briefly explain how to interpret the stack data, I would be more than grateful, I haven't a clue what to make of it!
Hey, I even remembered to switch to English!!!
Hello RMA;
I don't know if this info adds anything to what you already know, but just in case:
Hope this helps,
Daniel Chartier
Event id 2529 help as follows:
Cause:
A bit address (bits 0 to 2) was specified for byte, word, or double word access.
That's what puzzles me, because I've already used the value in "Pntr" - the base address of the UDT in the DB - successfully to store the WT-number and the date and time. When I go to use it again with Offset P#8.0 I get the above mentioned error - weird!
This is the first time I am working with Simatic Manager Step7 as I started my siemens journey with TIA which is pretty easy and do a lot of stuff...
146
When you download a DB, the values get overwritten by what is in the "actual" column in offline DB. Does this happen at the start of the PLC...
143
Hello Inside a FB, I´m trying to transfer a string from a DB to a IN_OUT var that was define as a UDT. The problem is that i can´t determine the...
137
Hi all, I am trying to convert RSLogix 5000 program to Step7. I need to bit shift left my array of double integers for tracking the product on...
525
I have a word in some DB which I want to load to AR1 and use as a pointer. In order to do this I need to write L DBxy.DBW xy SLD 3 LAR1 I...
541