Step7-Cyclic interrupt time-OB35
laura
Jul 2006
Torshavn
79
Hello.
If I set up the Cyclic Interrupt block OB35, to be 50ms........does anyone know, if this time varies........I mean, if there is a tolerance in it, so that in one sample it will be called at fx. 49 ms, and another at maybe 51ms ? Or will the block be called exactly evry 50ms each time ??
I believe it will call at the end of the current block that is processing, which normally be looking at micro seconds.
In your case as there will probably be no code in OB1, the error will be down to the PLC clock accuracy. You can expect more or mess 50ms.
edit: have you ensured that OB35 is to be called every 50ms, do this by looking at the CPU properties in the hardware profile under cyclic interupts.
Dear PeterW.
Yes I do it in the Hardware Profile, and it is right, that I do not have anything in my OB1.
The only thing I have, is that my OB35 calls my FB10 which, as You know, messes with datablocks.
So You say, that I can expect, that the recording and playing will take event exactly every 50ms ?
is there any free trial version available for step7 professional and wincc comfort v17. i searched and downloaded TRIAL Download STEP 7...
80
Hello. I need your help. I work at STEP7. There are two CPU 317-2 PN/DP controllers (317-2EK14-0AB0), working on PROFIBUS, as Master (CPU_1) and...
191
This is the first time I am working with Simatic Manager Step7 as I started my siemens journey with TIA which is pretty easy and do a lot of stuff...
182
When you download a DB, the values get overwritten by what is in the "actual" column in offline DB. Does this happen at the start of the PLC...
163
Hello Inside a FB, I´m trying to transfer a string from a DB to a IN_OUT var that was define as a UDT. The problem is that i can´t determine the...
164