I hope someone can help me to solve this rather weird problem.
When I compile the hardware config I get an error to the effect that I have configured too much I/O for some of my devices. As far as I can see, it's not possible to do that as there is only one input and one output address to fill in, the range being automatically calculated.
My environment...
Step 7 v5.5 with SP4
Windows 7 professional (64bit)
CPU 315-2 PN/DP
Problem devices are Siemens RF180C RFID communication modules connected via profinet.
The error I get is reproduced below (Repeated for each of the 29 devices). The addresses configured for this device are:
I addr: 256..259
Q addr: 256..259
Code:
Device OP10000-150E1 uses 7 input bytes and 7 output bytes. However, it permits a maximum of 4 input bytes and 4 output bytes including the accompanying user data. The sum must not exceed the value 8.
Consistency Check (13:5625):    The data length on the device "OP10000-150E1" has been exceeded. It uses7 input bytes and 7 output bytes. The sum must not exceed the value of 8.
Consistency Check (13:5235):    Input or output data length exceeded.
I will be grateful for any help with this.
Best wishes
Ian.
I just tried to copy an RF108C from Siemens sample project to a test project in Simatic Manager, and then I compiled it.
Went without a hitch.
You can set the start adress but not the number of bytes, which seems to be fixed at 4+4.
Something is messed up in your STEP7 project.
Start all over.
Copy the RF108C from the sample project to your project, and then see if you can compile for just 1 unit.
Thanks for your suggestion. It seems the sample uses a different version of the GSD file which works fine. I think the problem is solve.:D
Hello People. Me and a couple of other people are having some difficulty getting WinCC working. We have created a project in step7 controlled by...
7,026
This is the first time I am working with Simatic Manager Step7 as I started my siemens journey with TIA which is pretty easy and do a lot of stuff...
149
When you download a DB, the values get overwritten by what is in the "actual" column in offline DB. Does this happen at the start of the PLC...
145
Hello Inside a FB, I´m trying to transfer a string from a DB to a IN_OUT var that was define as a UDT. The problem is that i can´t determine the...
140
Hi all, I am trying to convert RSLogix 5000 program to Step7. I need to bit shift left my array of double integers for tracking the product on...
527