Hi to all. We connected a PLC that uses servos and encoders to a Stratix 5700 to nat its address so we can connect it to our administrative network. When we powered up the Stratix, the servos went to fault (LATE CTRL UPDATE). After checking the documentation and the Advanced time sync screen it turns out that the Stratix become the Grandmaster clock, so we decrease the priorities of the Stratix, the PLC becomes the grandmaster and all is working fine. Now we want to connect two more PLCs with their own servos and we want to avoid the same problem we had earlier. Is there a way to tell each PLC/servo to get the time from their own PLC and not from the other PLCs on the network or the stratix 5700? Or is there a way to them to share the stratix as the grandmaster or default to their local PLC in absense of the stratix without going to error?

New Network.png
 
Give each PLC different priorities. From memory, the PLCs have logic in their firmware to prevent issues with small time changes

With CompactLogix, you cannot turn this function off
 
We connected a PLC that uses servos and encoders to a Stratix 5700 to nat its address so we can connect it to our administrative network.

Kindly, you mentioned that you connected the switch to the outside network.
I am trying to do the same, using the G1 port with a fixed address.
But the switch is acting as a DHCP server, giving ip addresses to the offices laptops! even after we disabled the dhcp.
Did you have some issues with it?
 
Kindly, you mentioned that you connected the switch to the outside network.
I am trying to do the same, using the G1 port with a fixed address.
But the switch is acting as a DHCP server, giving ip addresses to the offices laptops! even after we disabled the dhcp.
Did you have some issues with it?
Kataeb, hi. Of course can access the Stritx's web server and disable the DHCP server, and add a static IP address.
 
Kataeb, hi. I downloaded the MS word file you sent. It shows the configuration of the static IP address and the DHCP function not-checked as you need. But I do not see in this file the screen where you save the configuration and where the switch is reboot. Did you perform these two steps?
 
Unfortunately I do not have this switch with me, so I cannot be 100% user. It seems it is the correct way of doing it.


Does the switch keep the same IP static configuration? If yes, then there is another DHCP server in that network. You will need to use Wireshark and capture the network packets. For this, setup the PC with dynamic configuration and start wireshark to see the MAC address of the host that is sending the DHCP settings.
 
Plugging your machine into the administrative network is a bad idea without a plan and network structure.

If you are only interested in EtherNet/IP communications, then you should configure the physical port connected to the admin network to only pass TCP Port 44818 and UDP Port 2222.

This will not allow DHCP to pass between machine network and admin network. You could create other rules as necessary.

Alternatively, you could use a NAT to only pass the devices you are interested in communicating with via the admin network.
 

Similar Topics

Kindly, if we enable the routing on the Rockwell Stratix 5700 switch, as in the below link, will it cause any trouble? Like for axis motion...
Replies
3
Views
165
Hi Guys, I have a Stratix 5700 managed switch that will connected to another different network thus: Stratix 1 on 10.50.3.xx >connect through...
Replies
0
Views
128
Hi Folks! Could I use the Studio 5000 to read/monitoring Stratix 5700 parameters? Like switch temperature for example
Replies
11
Views
394
Hi All, I've been playing with 2 stratix switches in my test bench and seeing how different configurations affect the behaviour when 2 managed...
Replies
3
Views
242
Hello, I added Stratix 5700 switch (rev13.001) to Studio5000 (rev 33.02.00) as Ethernet Module but it shows mismatch/yellow triangle on the module...
Replies
6
Views
286
Back
Top Bottom