You will need a MSG instruction. GSV/SSV instructions are only for getting data from or to the CPU. Use the MSG for any other device. Something like this.
CIP Generic
Class 35
Instance 1
Attribute 1
Specify a DINT destination Tag
Yes, this is the temperature in Celsius. The information comes from the EDS file.
21 = Class Code. The next two (20 means one value, 21 means two) values are the class. 5F and 03 is the class. Those must be swapped, so 5F 03 becomes 035F
24 = Instance. The next value is 01. That becomes the Instance
30 = Attribute. The next value is 01. That becomes the Attribute
OG
Following from JaxGTO, if you search in Rockwell's site for Network library, there is a library with a Stratix instruction as well as the DLR monitoring instruction.
If you're using FTView, there are faceplates, otherwise you may need to reverse engineer some of the parameters internally or the faceplate to get at that data.
I got it, guys! Thanks for share this knowledge. I solved my problem, using MSG instruction to get data through the parameters from EDS file. I saw the library with a Stratix instructions to create a faceplate using FTView too.
I am in process of implementing a new network to separate the manufacturing floor from the Enterprise network. See attached basic diagram. I have...
958
Greetings, I had an issue with a RIO rack 2 and IFM I/O Link dropping on my network. I would loose connection for a second or 2 then they would...
104
Kindly, if we enable the routing on the Rockwell Stratix 5700 switch, as in the below link, will it cause any trouble? Like for axis motion...
191
Hi Guys, I have a Stratix 5700 managed switch that will connected to another different network thus: Stratix 1 on 10.50.3.xx >connect through...
144
Hi All, I've been playing with 2 stratix switches in my test bench and seeing how different configurations affect the behaviour when 2 managed...
259