I know this is something that is done all the time... I think I've used it before communicating with a VFD. But right now it's not making sense, and I don't program everyday. I'm struggling to see what has gone wrong.
Test_REAL is a Float
TEMP01 is an array of DINTS
POC is an array of DINTS
POC is a real-world thing that I'm working with. It's a communication array made of DINTS. For the REAL values, the value takes up two DINTS, but the arrangement is opposite:
TEMP01[0] gets moved into POC[1]
TEMP01[1] gets moved into POC[0]
I loaded this into the customer's PLC, feeling confident it would work as expected. The I put a place-holder REAL value with a value of "0" in the place where Test_REAL is in this example. I ended up getting -5741 for the TEMP01[0] value, and 16783 for the TEMP01[1] value. So, I came home and did the same on my CompactLogix L16ER. The value of Test_REAL is 100. Does this look right to you? (attached, below)
Then, what is the way to re-assemble the two array DINTS back to a REAL? There's something with the order of the two DINTS, but I'm just not finding it and I've run out of spare time.
You seem to be saying that
- Test_REAL is a floating-point balue
- Test_REAL has the same footprint as two DINTs
Since DINTs are 32 bits (4 bytes) each, Test_REAL has twice 32, or 64, bits (8 bytes).
If Test_REAL is a floating-point value, then it should be double-precision i.e. an LREAL.
Also, are you are saying that if Test_real is 100.0, then the two DINTS you get are 1120403456 and 573645373?
cf. https://literature.rockwellautomation.com/idc/groups/literature/documents/rm/1756-rm006_-en-p.pdf#%5B%7B%22num%22%3A2009%2C%22gen%22%3A0%7D%2C%7B%22name%22%3A%22XYZ%22%7D%2C52%2C704%2C0%5D also https://literature.rockwellautomati...{"num":6986,"gen":0},{"name":"XYZ"},45,604,0]
Update II
  • Zero (0.0) in floating point, whether REAL or LREAL, must yield all zeros in all COPied-to DINTs.
  • So if you got -5741 and 16783 as the DINTs COPied from a floating-point value, then that floating-point value was not zero (0.0),
Update I
Okay, there is at least one problem: Test_REAL should be an LREAL if it actually does take up the same space as two DINTs;
See the Python example below: the 32-bit DINT decimal value 1120403456 is 42c80000h in hex, which is the same hex sequence as the 32-bit REAL decimal value 100.0; the 64-bit LREAL decimal value 100.0 has a very different hex sequence*
Code:
% cat z.py
import struct
temp01 = 1120403456,573645373
print('\n### {0} and {1} as hex:'.format(*temp01))
print('{0:08x} {1:08x}'.format(*temp01))
dbl = 100.0
print('\n### {0:.1f} 64-bit double-precision floating-point (Studio5000 LREAL) as hex:'.format(dbl))
print(''.join(['{0:02x} '.format(ord(s)) for s in struct.pack('>d',dbl).decode(encoding='8859')]))
print('\n### {0:.1f} 32-bit single-precision floating point (Studio5000 REAL) as hex:'.format(dbl))
print(''.join(['{0:02x} '.format(ord(s)) for s in struct.pack('>f',dbl).decode(encoding='8859')]))
print('')
% python z.py
### 1120403456 and 573645373 as hex:
42c80000 2231223d
### 100.0 64-bit double-precision floating-point (Studio5000 LREAL) as hex:
40 59 00 00 00 00 00 00
### 100.0 32-bit single-precision floating point (Studio5000 REAL) as hex:
42 c8 00 00
* although 42c8h is identical to 4059 if the former shifted 3 bits after the initial [4] bit, to account for the 8- vs. 11-bit exponent difference between REAL and LREAL:
Code:
42c8 => 01000[COLOR=blue][B]0101[/B][COLOR=Red][B]1001[/B][/COLOR][/COLOR]000  REAL
4059 => 01000[U][COLOR=orange][I][B]000[/B][/I][/COLOR][/U][COLOR=Blue][B]0101[/B][COLOR=red][B]1001[/B][/COLOR][COLOR=black]  LREAL[/COLOR][/COLOR]
[I][B][COLOR=orange]              ^
              +-- shift of 3 extra bits for LREAL exponent[/COLOR][/B][/I]
I've never really dealt with REALs on this level, but from what you are saying the data will be coming in as 64-bit (two DINTS), is this correct?
Afaik, Logix only supports 32-bit REAL values.
Your COP then has a source of 32 bits (one REAL), but a destination of 64 (two DINT). To fill the remaining 32 bits it will simply grab whatever is next in controller memory.
If you've got a tech connect contract, see https://rockwellautomation.custhelp.com/app/answers/answer_view/a_id/36632 for some help converting from a 64-bit to 32-bit
To summarize, there is no way to COPy two DINTs into one REAL.
You can COPy one DINT to one REAL, or you can copy two DINTs to one LREAL.
Without knowing the format or data type your receiving device is expecting as a SP, it's hard to offer any advice.
It's unusual anything is going to need a SP comprising of 2x DINTS.
Post a bit of the manual explaining what it needs.
Hello Guys, I have just upgraded an older machine from a old processor to a new studio 5000 processor (1756-L83ES). For some reason when I am...
3,647
Hello. I used to do this all the time in older versions of RSLogix 5000. I could copy and paste from my UDT to excel, make changes, and then copy...
5,220
Question about COP and UDT's in Studio 5000. I have a UDT structure with various data types that is reporting (according to the properties tab in...
2,511
Hi, I have a maybe simple question but I don´t know a solution so far.. I have a UDT which contains a lot of BOOL variables. Now i want to copy...
6,794
Hi Everyone. Not posted on here for a long time, but I am hoping someone can help me. I am doing a differential pressure calculation in a L27ERM...
294