Studio 5000 Online Tag Copy Paste
kevilay
Feb 2009
Ontario
174
Hello Guys,
I have just upgraded an older machine from a old processor to a new studio 5000 processor (1756-L83ES). For some reason when I am online I cannot copy paste tags. I was doing it no problem on RSLogix 5000 & I was almost 100% positive I have been able to do it in studio in the past. We are running V31.
Any suggestions?
Thanks,
Kevin
If you are doing online edits you must first double click the rung you want to paste to, the rung will show an in edit state. Then you can paste, then accept and finalize the edit of the rung.
I was actually referring to copy and pasting tags in the tag edit screen. Not actually ladder logic. Normally you would copy paste it and it would add a 1 to the end, then you could rename it to what you want.
Similar situation applies. At the bottom left of the tag window you would need to be on “edit” tab and not the monitor tab. Have you tried that?
Yes I was definitely on the edit tab. When I right click I just cant select paste.
Ever since I had to change PCs and redownload all my AB software I have been unable to go online with a controller via Studio 5000. I used to be...
1,149
I have a device that is communicating to ControlLogix L83E. During apply of online edits to plc, the communication to the device is increasing 4-7...
1,186
Good Morning , I went to edit a rung , and for some reason I can “ Accept Pending Rung Edits “ , but I can’t assemble rung . I...
17
6,342
Hi All, I am having an odd issue, need help now!:bawling::bawling::bawling: The studio version is 32.13, drive add on is 5.08. PLC is l36erms...
1,860
After migrating a SLC to a 1769-L36ERM, the Studio 5000 interface was almost unusable. I started with v24, and then changed to v30 with no...
6,420