Shawn Member S Join Date Oct 2003 Posts 24 Oct 19, 2003 #1 Hi everyone, when I open a new project in Rslogix5, How I can define my PLC CPU as SLC 5/01?I can't find SLC 500 serials in the processor list. Thanks
Hi everyone, when I open a new project in Rslogix5, How I can define my PLC CPU as SLC 5/01?I can't find SLC 500 serials in the processor list. Thanks
LadderLogic Member Join Date Jun 2003 Location Chicagolandia Posts 1,486 Oct 19, 2003 #2 Don't you need RSLogix 500 to work with the SLCs? RSLogix 5 is for the different beast. Or was it just a typo?
Don't you need RSLogix 500 to work with the SLCs? RSLogix 5 is for the different beast. Or was it just a typo?
randylud Member R Join Date Oct 2002 Location Greensboro,NC Posts 933 Oct 19, 2003 #3 Wrong number? when I open a new project in Rslogix5, How I can define my PLC CPU as SLC 5/01? Click to expand... You can't! As LadderLogic pointed out you need RSLogix500 for the SLC/Micrologix family of processors. RSLogix5 is for the PLC-5 family. Get it? 5 vs 500 !!
Wrong number? when I open a new project in Rslogix5, How I can define my PLC CPU as SLC 5/01? Click to expand... You can't! As LadderLogic pointed out you need RSLogix500 for the SLC/Micrologix family of processors. RSLogix5 is for the PLC-5 family. Get it? 5 vs 500 !!