Suspect profibus problem - how do I proceed?
Pete.S.
Mar 2016
Fl
463
Hi guys,
I have a machine that has been acting up a few times lately. It looks like it "forgets" it's position.
The position comes from a profibus connected absolute encoder. The profibus cable is run in a cable chain where it goes a couple of feet back and forth, maybe three thousand times in a day, every day of the year.
The PLC is a Siemens CPU 315F-2 PN/DP and the encoder is the last device on the profibus.
  • My wild guess is that there might be an intermittent problem with the encoder or the cable to the encoder. Is this likely?
  • What happens if there is a problem with the cable and the plc and encoder doesn't communicate for a second or two? How is an error detected and what happens in the cpu? What would happen to encoder value in the plc during this break in communication?
  • Also is the profibus cable even suitable to have in a cable chain for something that moves all the time? Or is this bad solution?
  • How would you troubleshoot this problem?
Thanks in advance for any input or ideas you might have!
Best Regards,
Pete
In a Siemens S7 PLC, an error-OB is triggered.
Investigate the diagnostics buffer.
Depends on the setup of the encoder parameters. It may keep its last value. Or it may be set to zero.
Plain Profibus cable no. But there are Profibus cables for every application. Investigate the brand and type of the cable.
Look for cable or connector problems.
Checkup that there is a good equipotential earth.
Checkup that the screen is clamped to a earth, not only in the connector.
If nothing is revealed, try to exchange parts and see if the error disappears or moves.
If still nothing, consider renting or buying a profibus diagnostics tool.
Hi All, I have been working on a home rig that has a 1756-L61S and the relevant safety partner. Have owned for a long time and never had any...
2,186
Hello, I have a DB (22 gigs big) that is suspect and not working anymore. I found this repaircode on internet: EXEC sp_resetstatus SOADB; ALTER...
4,684
I have a 1769-SDN DeviceNet scanner attached to a MicroLogix 1500, flashing 75 63. (No traffic, node 63). The highly suspect part is that the...
2,396
I currently offshore on a platform doing a pre-start check of some equipment and I have a pressure xmitter that's causing the Underrange bit to...
3,565
Hi, I was noticing that Profibus connectors have 2 ports on them that can house 2 separate cables. Can I use 2 cables with Profibus signals...
190