Temp analog to PLC
Hammeraven
Dec 2008
SD
I'm helping some students work on a project and could use some advice.
The project is a ethanol still that the students built. The idea is to get the process semi-automated. I am a PLC programmer and have limited knowledge on what components I should be using as inputs/outputs. I also know that using a PID would be ideal, but I guess that is not an option to purchase right now :(
So what I am using AB MicroLogix 1400 series PLC (4 analog inputs)
some discrete inputs/outputs (pumps, buttons etc)
What I need is an analog temperature sensor (0-10V ) for reading stack (steam I believe) temp and reading water/mash temp in the tank. (not sure if I can use the same kind of sensor or not)...if anyone could recomnet a specific brand I would appreciate it...there are so many options, just not sure of the right one! Thanks!
The 0-10Vdc analog inputs are 'high level', so temperature sensors can not connect directly.
Standard industrial temperature sensors are
- thermocouples, millivolt output which need 'cold junction compensation' for any reasonable accuracy.
- RTD's that are resistive elements, require a constant current 'excitation' source (less than a milliamp)
Thermistors are also resistive elements, but require an input capable of reading resistance by sourcing a current and reading the voltage drop; or an external voltage source that creates a voltage drop (which an analog input 'reads') by sourcing a constant current.
The typical approach is to use a temperature sensor along with an industry standard 'transmitter' which converts the temperature sensor signal to an industry standard range, like 4-20mA or 0-5Vdc or 0-10Vdc. An industrial transmitter requires a separate power supply, typically a 24Vdc power supply.
4-20mA is sooo common, that frequently a precision resistor is used to create a 1-5Vdc (with a 250 ohm) or 2-10Vdc (500 ohm) signal (Ohms law).
Many PLCs have modular cards which accept temperature sensors directly. I don't know if the 1400 does or not.
The TP RTD here: http://www.ifm.com/ifmus/web/temp-ia-2.htm might have both an RTD and a transmitter in one assembly, it isn't clear.
But at $78 it might be worth checking into. Most RTD's cost around $78 by themselves.
Gentlemen, I am using an Omega 5550 temp ir with 4-20 input to plc. Trying to display the temp value has been discouraging. The displayed value is...
4,891
Hello, I'm working with a 1747-NI4 analog input module (for the first time) on a SLC503 processor. I noticed in the IO configuration within...
4,771
Any way to read a thermistor/thermocouple on a GE 90 Micro Analog Input? 0-10V, 0-20mA or 4-20mA? I tryed with a LM35DZ chip which give 10mV/*C...
3,771
The objective: Reach about 10’ horizontally into a 1300F furnace, and pick up a 140lb rectangular container, then pull the container back out of...
1,881
Hi Everyone, We have Silo System which has temperature sensor and these sensor data will be communicating through RTU unit to the Dedicated PC...
620