Temperature process Slc 5/04
Adam303
Aug 2009
Chicago
587
Hi to all Again
I have a frezzer tunnel that used liquid nitrogen to freeze product.
I have to redesighn the tunnel because it looks like it came out of a junk yard. For the project we first wore not going to use a plc but now we came to a concusion we should.
I have most of the programing done but i'm stuck at few points.
For the Slc 500 7 slot rack i'm using the following:
slot o 5/04 processor
slot 1 1746-iv16 input module
slot 2 spare
slot 3 1746-ow16 output module
slot 4 spare
slot 5 1746-nio4i analog combination module
slot 6 1746-nr4 rtd module
The analog output 4-20 will be proportional to process temperatue and will drive a electronic to pneumatic controller. The controller than will have a proportional output of 3to 15 psig and will regulate a pneumatic valve that will open the liquid nitrogen.
The rtd will have two inputs (pt100) one for low temperature
limit (set At -280 F) The second will reed the process temperature.
The problem
Now i have to write a pid instruction but i'm not so sure how to adress it
In the pid intruction should the process veriable be the input of the 1746_NR4 module or should i take the output from NR4 (scaled from 0 to 16383) copy it to a inager and than place it to the process verible??
I also have to be able to write to the pid instruction to change the Sp set point.
Does any one have pdf file of a program using the hr4 rtd module and a pid instruction
you should use 0-16383 scaled value of the temperature for PID instruction input (PV - process variable). PID output also will be scaled 0-16383 (if i'm not mistaken).
The problem
Pardon this it does not make any sense to me so how would it make any sense to any one eles.
let me clear this up.
IN the process verible I have to use scaled 0-16383 from the input of the 1476-nr4
Data transmitted from the module to the processor is called the input
image (for example, Channel Data Words and Channel Status Words).
Conversely, data transmitted from the processor to the module is
called the output image (for example, Channel Configuration Words​
and Scaling Limit Words).
Ok so now I have the Process verible scaled for pid 0-16383
Since the pid control verible is also scaled 0-16383 how would I scale this to be a 4-20 output?????
This is way OT and not meant to be a putdown or any type of insult only an observation, but are you a Master Electrician over the age of 40?
You certainly spell like the Master Electrician we have on staff, a brilliant guy, but horrible with the command of the English language on paper.
so should i just address the control variable as an O:3.0 ??
Our core group is almost as large as any major company out there in the automation field
What can I Say ESL It is also sad that a specialist like you with a huge backgroung in automation can give such a huge feed back. But the only thing keeping me happy about this is that at some point in time You had the same knowledge as I do today.
For the current output:
0 digital = 0mA
3277 digital = 4.0mA = 3.0 psi
16384 digital = 20.0mA = 15.0 psi
I suggest you take the output of the PID and scale it to a floating point value that represents the engineering units (psi) of the final control element. That way you can verify your scaling throughout the controls.
You could then take the psi units and scale again to get the 4-20ma (3277-16384) or use the PID output directly and scale it.
Have a look at the SCP instruction (scale with parameters). It does all the work for you.
Paul
Like I said, I did not mean to offend, I just had a chuckle.
Also if you are using an air actuated proportional valve, ensure you have a Burkert style shut off valve upstream from the valve, and use an air solenoid to feed the I/P. One solenoid can be T'd for both and only actuated when you need the cooling. What this does is prevent any trickle cooling medium getting through when the process is not in use. Almost every 3 - 15psi controlled Jordan style proportional valve will eventually leak.
Hi all, Trying to find a pressure sensor for an application where the process is running at -100°C (-148°F). Pressure is likely around 1 bar or...
2,943
Here is our latest post that we would like to share. Modbus RTU will be the serial (RS485) method in which we will communicate between the...
1,467
Is it possible to use the standard PID control of Siemens (step7) to control a 3 step temperature process. Of do I have to buy their Standard PID...
1,521
I am planning to simulate a temperature loop and a pressure loop using PIDE functions blocks in ControlLogix. I used a dead time + first order lag...
5,239
Have a question that I hope someone can help with. Have been looking into using a Omron Process Controller to possibly control a I/p tye valve for...
5,144