Hi all,
Where I work, we make a lot of hydraulic power units with three phase motors. We test each of these and so are constantly hooking up motors on a temporary basis. We are in the process of upgrading our testing area to provide more ease of use and better protection for these temporary electrical hook ups.
I'm wondering if anyone else is in this situation and if so, do you have any methods or practices to share regarding what you like or don't like in your set ups.
One think we have in our system that we will be carrying over to the new system is a built in Hi-Pot tester/interlock on each motor starter from Meg-Alert. We occasionally do re-work of older equipment and after finding a couple bad motors the hard way, installed these.
Ideally, I could have 4 or 5 hook ups with programmable outlet ports for different motor horsepowers.
Make a clamp that fits over the boltcap, so you do not need to tighten the bolts every time.
First use the megger to check the motor.
Then start a nice big VFD, you can control the max current very easily on the keyboard.
If too high it will stop unit, without damage.
You can even make a graph how much current is drawn under load etc.
We use terminal blocks on DIN rail and keep a locked local disconnect for each voltage we use. This way the current is physically covered up and locked out with a shop gang lock when not in use. Do this with your VFD's too. Run all the wiring to terminal blocks so that all you have to do is hook 3 wires up to terminal blocks and hit a switch/disconnect to see the motor under load.
In these times of isolation I thought it might be fun for us to own up to past temporary fixes that we, for 'whatever reason' never got back to...
2,701
I have one strange issue, I'm not experienced enough to understand. We have generated one FC for scaling and writing to analog outputs, which we...
6,595
I have project converting a PLC5 to Controllogix and 1734 Point IO. I am looking for a pro to help with this conversion. You should have your...
1,289
In all our programs written with Step 5 (come to think of it, all our programs. Full Stop!)we use 'temporary flags', these are flags that are used...
5,176
I'm looking for how others do it. I need to start a 1 phase motor. I have always used a regular 3 phase Motor Protected Circuit Breaker and looped...
140