temprature increase per min
This could get tricky depending on the thermal mass of the furnace contents and the energy capacity of your heaters. Expect a fair amount of dead time in your control response.
I'd calculate the rate of change as Dravik suggests. ROC = ΔT/Δt. The time interval t will have to be based on observation. You will need to have a long enough interval to get an accurate rate, but not so long your control can't respond.
I would use the ROC as the process variable for your control loop, with heater power the controlled variable. Then, when you get to, or close to, set temperature switch to another control loop with the actual temp as the process variable.
here I m controlling tt 31 by plc by changing 4-20 ma manually.
n tt 32 is controlling by a programmable meter.
Time TT_31.PV TT_32.PV
7:24:00 PM 1,289.23 1,272.82
7:18:00 PM 1,317.76 1,298.24
7:12:00 PM 1,344.13 1,324.53
7:06:00 PM 1,367.01 1,350.55
7:00:00 PM 1,393.97 1,376.97
6:54:00 PM 1,418.20 1,402.19
6:48:00 PM 1,443.97 1,429.03
6:42:00 PM 1,472.52 1,455.96
6:36:00 PM 1,495.40 1,483.16
6:30:00 PM 1,493.69 1,506.82
6:24:00 PM 1,480.25 1,504.32
6:18:00 PM 1,464.87 1,483.98
6:12:00 PM 1,449.06 1,464.25
6:06:00 PM 1,432.87 1,443.98
6:00:00 PM 1,416.19 1,424.76
5:54:00 PM 1,397.80 1,405.02
5:48:00 PM 1,376.97 1,385.35
5:42:00 PM 1,355.25 1,365.31
5:36:00 PM 1,336.53 1,346.18
5:30:00 PM 1,315.95 1,325.97
5:24:00 PM 1,301.39 1,307.52
5:18:00 PM 1,288.41 1,291.02
5:12:00 PM 1,274.86 1,275.00
5:06:00 PM 1,260.68 1,258.78
5:00:00 PM 1,246.54 1,241.60
4:54:00 PM 1,231.86 1,225.05
4:48:00 PM 1,216.74 1,208.51
4:42:00 PM 1,200.49 1,192.38
4:36:00 PM 1,182.44 1,175.78
4:30:00 PM 1,167.70 1,159.30
4:24:00 PM 1,152.65 1,142.58
4:18:00 PM 1,136.45 1,125.83
4:12:00 PM 1,118.94 1,109.50
4:06:00 PM 1,100.95 1,092.39
4:00:00 PM 1,084.16 1,074.90
3:54:00 PM 1,069.04 1,058.57
3:48:00 PM 1,051.32 1,042.44
3:42:00 PM 1,033.54 1,024.69
3:36:00 PM 1,016.99 1,008.85
3:30:00 PM 1,017.79 994.17
It would help to take the data you are getting and map the response of the heat up for various output power settings.
Should give you an idea what the heater ramp looks like from a 'general' perspective. Use that to baseline where you'd expect power output to need to be and what your response time will look like for changes.
Dear all! I am trying to Communicate with one temperature controller(Honeywell DC1040) using Miglogix1500&1769sm2 module via Modbus...
5,715
hi every body i'm facing problem in completing plc program which control burner through servo motor (control gas flow) analog output (0-10V) so i...
5,337
Sirs, Please any body help me for Temprature controller in GE fanuc PLC. I don't no how to do this job in GE Fanuc PLC.
5,168
What has been your experience with year over year price increases on your Tech-connect service contracts? Is it up to the distributor? 30% seems...
288
I want increase the length of string from 82 to 150. By default it comes 82 is it possible to do so in Studio 5000
628