Test setup for a 162-IF4
With the internal resistance of each channel at 275 ohms, see picture below. The current will be about 8ma ( 7.7ma ).
I would prefer to test each channel and be able to vary the current up/down myself.
Ohms law!
Thanks for that Mickey I was forgetting about loading and ohms law, so if I drop the 2k resister and used 900ohm would achieve my 12ma 50% fsd!
Git: cheaper option would be an LM317 at $2.50 2 diodes at 20c a resister at 6c and a 10k pot at $2.10 ! Aussie prices! total $4.86.
See picture below, its a snapshot of the manual for a 1771-IFE. I have seen this same note in other analog card manuals.
And a PDF for SLC input modules.
  • jumper1.pdf