Hi guys,
I have SLC500 1747-L40E brick with sinking inputs. If I understood Terry Woods NPN/PNP posting correctly (image #9) would'nt I use NPN sensors & proxes as input devices? What confuses me, and frankly what doesn't, is I'm used to seeing NPN as sinking and in conflict with Mr. Woods' posting.
Thanks
 
Before I commit fully to my answer (which would be "no, you will need to use PNP sensors with sinking inputs" if I weren't such a coward), to what post of Terry's are you refering?

Steve
 
Last edited:
Earl29 said:
If I understood Terry Woods NPN/PNP posting correctly (image #9) would'nt I use NPN sensors & proxes as input devices? What confuses me, and frankly what doesn't, is I'm used to seeing NPN as sinking and in conflict with Mr. Woods' posting.
Thanks

Earl,

Scroll down to the bottom of the Patch.net link. You will see in the last example that NPN or PNP transistors could be used as Sinking or Sourcing devices depending on their oriantation in the device. Just because a particular device uses a NPN transistor output, it does not necessarly mean it's a Sinking or Sourcing Device.

Just keep in mind the following: If the input or output on the PLC is a Sinking I/O then the device connected to it will be a Sourcing Device; and visa versa.
 
41abc35519c8077b.gif


My drawings reflected all of the possibilities. There was a time when the selection of available sensors was very small... in those days we made our own. The drawing is valid in terms of possibilities.

However, since sensor manufacturers appear to have settled on a particular configuration for sourcing (the PNP form... think Peein'-N-Peein' as in sourcing... think of that kid peein' on the Ford or Chevy Logo) and sinking (NPN... Not PeeiN), you are most likely (these days) to use a PNP (Peein'-N-Peein') Sourcing Sensor to feed an NPN (Not PeeiN) Sinking Input.
 

Similar Topics

I have an old Sentry Palletizer (S/O Number 3007 / Serial Number 1172) that has lost its program as the backup battery died years ago. I can...
Replies
0
Views
107
This is admittedly a pretty obscure problem, but maybe someone else has run into it, or at least something similar. For reasons I won't get into...
Replies
3
Views
147
Does Rockwell still offer reset codes for old school Master Disk floppy's? In a bind and need to reset the activation disk soon and to be pointed...
Replies
9
Views
257
Has anyone found a way to convert/replace/update the firmware on old Parker TS80xx series HMIs (i.e. TS8010, TS8006, etc) to accept Crimson...
Replies
0
Views
105
Hey all, I am currently working on a depalletizer for a customer and we are doing a hoist upgrade. This is a SLC500 processor and the drives are...
Replies
6
Views
321
Back
Top Bottom